Not always a fault of the wiring. PVC doesn't fail that easily under normal usage. It could be 1/ New new light fitting 2/ An appliance still plugged in 3/ Class II spd somewhere. 4/ DIY tinkering I chased a fault around a commercial garden set up for a week and discovered that the IR was down because of a combination of a couple of convector heaters used to warm up the green houses which had automatic sprinklers installed and two faulty fountain pumps. She was very reluctant to accept her B&Q heater solution was the problem and was convinced that all the wiring had failed. Legh ------------------------- Why do we need Vernier Calipers when we have container ships? http://www.leghrichardson.co.uk "Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections." |
|
|
|
|
|
|
|
|
well, the last dead mouse frying in the terminal box I tested last week threw out about a 0.4M reading, so I would say yes, investigate.
|
|
|
|
|
|
|
|
|
well, the last dead mouse frying in the terminal box I tested last week threw out about a 0.4M reading, so I would say yes, investigate. i took the lid off of a cu a couple of weeks ago and there was a mouse straddling the tails. i nearly fell off my steps. Gary ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
|
|
|
|
|
|
|
|
Ah, another good point to consider for the working at height risk assessment Across the incoming terminals of electric cookers used to be a favourite of theirs (I guess they went for the warmth). - Andy. |
|
|
|
|
|
|
|
|
Ah, another good point to consider for the working at height risk assessment Across the incoming terminals of electric cookers used to be a favourite of theirs (I guess they went for the warmth). - Andy. Surely, once the mouse has 'boiled' down the IR should go back up again, so a temporary IR glitch wouldn't you say? Legh ------------------------- Why do we need Vernier Calipers when we have container ships? http://www.leghrichardson.co.uk "Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections." |
|
|
|
|
|
|
|
|
Hi Pat. i am going to assume your installation is a 230/400v installation and you got your results from a periodic inspection.
if all this is true none of your readings would meet the requirements for insulation resistance from GN3 (1Mohm). one of the readings is a dead short. If it is a periodic you were carrying out i would give a C2 as though the readings are all very low the installation im assuming has been in some condition of working order, perhaps with the exception of the dead short reading. if this was an initial inspection personally i would C1 all your readings as they are so low i couldnt take account for any degrading over time. in any case all your readings would warrant further investigation. these are of course my own personnal opinions. I wouldnt be happy leaving any installation with those IR readings I would have to find out whats causing them. |
|
|
|
|
|
|
|
|
If it was an initial verification, there would not be any codes.
|
|
|
|
|
|
|
|
|
If it was an initial verification, there would not be any codes. Quite right Edited: 21 November 2012 at 05:39 PM by vesuvius |
|
|
|
|