could i have thoughts regarding the following;
switched isolator fed from ryfield with 16mm tails backed up at source with 40amp bs 88-2 . then from switched isolator 1.5mm mineral 4core 3phase supply to lift room where a fused isolator is installed with 16amp motor rated fuses. Current carrying cap = 19amps Zs = 0.38 between phase and earth Q1 is fault protection afforded. Q2 is overload protection afforded. |
|
|
|
|
|
|
|
|