Topic Title: EICR code for poorly earthed lights?
Topic Summary:
Created On: 11 November 2012 09:07 AM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 11 November 2012 09:07 AM
User is offline View Users Profile Print this message



alanblaby

Posts: 373
Joined: 09 March 2012

Chandelier type metal light fitting, R1 + R2 is 155 ohms at the bayonet/lamp fitting, less than 1 ohm when tested at the pendant connection (so fixed wiring is good).
Took off the fitting, and though there is an earth lead there, the end cannot be traced, but clearly seems to have a poor/loose connection.

I was thinking this should be a C2 (it is approx 2000mm from the floor when fitted), am I correct in my thinking?

Or maybe a C3?

Thanks
Alan.
 11 November 2012 09:54 AM
User is online View Users Profile Print this message



daveparry1

Posts: 6210
Joined: 04 July 2007

If anything i'd say C3 because it's not really dangerous is it. If it's on a 30m/a rcd no code at all though. (max. 1667 ohms)

Dave.
 11 November 2012 02:01 PM
User is offline View Users Profile Print this message


Avatar for sparkiemike.
sparkiemike

Posts: 1543
Joined: 24 January 2008

I would go with a C2. because the observed deficiency is not considered to be dangerous at the time of the inspection, it would become a real and immediate danger if a fault or other foreseeable event was to occur in the installation.