Topic Title: Safe use of a compression gland
Topic Summary: Regulations
Created On: 09 November 2012 10:51 AM
Status: Post and Reply
Linear : Threading : Single : Branch
<< 1 2 Previous Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 09 November 2012 06:02 PM
User is offline View Users Profile Print this message



Fm

Posts: 718
Joined: 24 August 2011

I thought it was a wimes spec, with the earth tags on the tray!
That installation wont comply with 3.02 wimes electrical spec.
 09 November 2012 06:54 PM
User is offline View Users Profile Print this message


Avatar for stateit.
stateit

Posts: 2204
Joined: 15 April 2005

Originally posted by: ewan29

They will be under investigation for a disciplinery and I had hoped that we could have found more than just poor quality workmanship and a disregard of the design to use in the disciplinery.


Sorry to be an @rse again (as usual).

OK - Didn't meet spec.

OK - Even if T&E and stuffing gland was specced it'd be ruff.

But for Crying Out Loud: Can't just a quiet word with the contractor sort this out? Why so rabid?

Any good manager (wrt your client) would be appeased with a gentle 'The situations being sorted and we won't be using that contractor again'.

You'll bust a blood vessel dear. Calm down.

'Nuff Said.

-------------------------
S George
http://www.sg-electrical.com
 09 November 2012 07:50 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4439
Joined: 10 December 2004

Is this by any chance at Beckton?
 10 November 2012 01:01 PM
User is offline View Users Profile Print this message



MrP

Posts: 846
Joined: 24 March 2006

"What reg does it break "


132.5 Environmental conditions is the T&E suitable for a water treatment facility ?


132.5 type of wiring and method of installation. the nature of the installation external influences(Mechanical stress)?


133.1.1 Every item of equipment shall comply with the appropriate British Standard I'm pretty certain the standard for stuffing glands will not say you can squeeze two cables into just the same as you can not sqeeze two T&E in one single T&E cable clip


134.1.4 Good workmanship shall be used. Electrical equipment shall be installed in accordance with the instructions provided by the manufacture of the equipment


Chapter 52

MrP Home in 39days
 10 November 2012 04:50 PM
User is offline View Users Profile Print this message


Avatar for stateit.
stateit

Posts: 2204
Joined: 15 April 2005

Originally posted by: MrP


133.1.1 Every item of equipment shall comply with the appropriate British Standard I'm pretty certain the standard for stuffing glands will not say you can squeeze two cables into just the same as you can not sqeeze two T&E in one single T&E cable clip/q]

While there is a BS for cable glands, I wasn't aware there is one for cable clips.

-------------------------
S George
http://www.sg-electrical.com
 10 November 2012 05:06 PM
User is offline View Users Profile Print this message



weirdbeard

Posts: 1579
Joined: 26 September 2011

I think the OP might have been better off titling his post - 'A contractor has used T+E when SWA was specified'

The stuffing gland issue seems pretty trivial in comparison.
 12 November 2012 10:28 AM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11553
Joined: 13 August 2003

133.1.1 Every item of equipment shall comply with the appropriate British Standard I'm pretty certain the standard for stuffing glands will not say you can squeeze two cables into just the same as you can not sqeeze two T&E in one single T&E cable clip

But 133.1.3 does allow equipment to be used outside of its standard - just provided that someone confirms that its no less safe that way. Is there a safety issue with two T&E cables in a gland?
- Andy.
 12 November 2012 09:57 PM
User is offline View Users Profile Print this message



Zs

Posts: 2977
Joined: 20 July 2006

If they are small enough to fit and for the grommet in the compression gland to take shape around them as it is offered forward, then I can't see what the problem is. 1.5mm T&E x 2 into a stuffing gland, IMHO, actually offers a better seal than 1 x 1.5mm T&E into a stuffing gland.

Just a comment, not trying to make waves.

Zs
 13 November 2012 06:21 AM
User is offline View Users Profile Print this message



MrP

Posts: 846
Joined: 24 March 2006

Did the designer state on the EIC that the make up of the installation was outside the scope of the Standard and if so how did he confirm and verify that the installation provided the same degree of safety
The gland is designed to accept one cable, so not adhering to the Standard if two cables are fitted how do you confirm that the compression is not to tight causing damage to the insulation and a breakdown in insulation resistance or to slack and not offering mechanical protection and possibly IP 4X
So is the installation a deviation or non compliant
For my two Riyals worth its non compliant

MrP 36days and home
 13 November 2012 07:14 AM
User is offline View Users Profile Print this message



Fm

Posts: 718
Joined: 24 August 2011

Tray cuy through at slots
No edge protection, grommett strip
Doesnt look like post galv roofers, is the unistrut?
No uni end caps
Earth conductor not termnated
Cables not ty rapped. Neatly
Penetration not sealed
Ip washers on glands?
Cable dents preventing visual inspection of glands?
Correct glands. E1w? Or cw or bw
Is this top entry into panel?