Topic Title: Need to know 702.55.1 and 418.3 please
Created On: 08 November 2012 08:49 PM
iwire
Hi
Would somebody be so kind as to quote me regulation 702.55.1 and 418.3 please.
I do not have an up to date bible at the moment and am desperate to read these regs.
 08 November 2012 10:14 PM
I'll start with 418.3 (702.55.1 is a bit long for my fingers at this time of night).
418.3 Electrical separation for the supply to more then one item of current-using equipment
Where the measure is used to supply two or more items of equipment from a single source, a warning notice complying with Regulation 514.13.2 shall be fixed in a prominent position adjacent to every point of access to the location concerned.
NOTE: Electrical separation of an individual circuit is intended to prevent shock currents through contact with exposed-conductive-parts that may be energized by a fault in the basic insulation of the circuit.
 08 November 2012 10:39 PM
sparkiemike
702.55.1 Current-using equipment of swimming pools
In zones 0 and 1, it is only permitted to install fixed current-using equipment specifically designed for use in a swimming pool, in accordance with the requirements of Regulations 702.55.2 and 702.55.4.
Equipment which is intended to be in operation only when people are outside zone 0 may be used in all zones provided that it is supplied by a circuit protected according to Regulation 702.410.3.4.
It is permitted to install an electric heating unit embedded in the floor, provided that it:
(i) is protected by SELV (Section 414), the source of SELV being installed outside zones 0, 1 and 2. However, it is permitted to install the source of SELV in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1, or
(ii) incorporates an earthed metallic sheath connected to the supplementary equipotential bonding specified in Regulation 702.415.2 and its supply circuit is additionally protected by an RCD having the characteristics specified in Regulation 415.1.1, or
(iii) is covered by an embedded earthed metallic grid connected to the supplementary equipotential bonding specified in Regulation 702.415.2 and its supply circuit is additionally protected by an RCD having the characteristics specified in Regulation 415.1.1.
 11 November 2012 09:39 PM
iwire
Thanks very much for this.