Evening,
Next week I shall be having the service head and meter relocated on my house which I have recently re-wired. - The original job has been certified and notified. It will mean installing new tails, and providing a switch fuse to provide protection for the tails as they will exceed 3m. In terms of testing and certifying this, am I correct in thinking that I will need to re-test all final circuits as well as the new distribution circuit, and issue an EIC with a full schedule of test results? - Obviously Ze and therefore circuits' Zs will almost certainly change, if only fractionally. Also, in 'extent of installation covered by this report' what kind of thing should I be writing to make it clear that it's just the distribution to the CU that is being installed? Thanks as ever, Dave. |
|
|
|
|
|
|
|
|
Hi Dave , not sure if you would need to retest the whole installation.
The R1+ R2 for the circuits will still be the same and insulation resistance will be unaltered. You will need to test the submain so I cannot see any reason why you cannot just add the additional R1 +R2 of the submain onto the circuits. I would personally Zs test all sockets. In the extent of installation box you could write " installation of new submain to consumer unit ". Regards |
|
|
|
|
|
|
|
|
If it's your own place so you know no one has "fiddled" since the last set of results. I'd do a cert for the sub-main and use the sub-main Zs as the starting point for a replacement cert for the house (if it's changed enough to worry about)
stu |
|
|
|
|
|
|
|
|
Cheers guys,
I was hoping someone would suggest it wasn't neccessary to re-test the entire thing, I think you're right, - as I did the original cert, I will be able to re-certify based on the original readings. Thanks, Dave |
|
|
|
|
|