Topic Title: Oven and hob
Created On: 26 September 2012 11:51 PM
GJH
Hi
Been to a job today where customer has bought a 6.8kw induction hob and seperate 4.2kw oven. The existing supply is a 6.0mm cable less than 10m from the fuse board.
Checking the onsite guide and applying diversity you take the first 10A of each cooking appliance current rating and then it's 30% of the remaining current rating + 5A if there is a socket on the outlet switch. Both units are hard wired from the manufacturers with what looks like a 2.5mm HR flex.
My calculations is that without a socket outlet on the switch it works out to about 27.8A.
I think the existing installation will be ok? But just looking for some reassurances or opinions. Or if I have got it wrong.
Customer is a young couple and house is pretty new.
Thanks in advance
 27 September 2012 08:30 AM
It will be fine GJH, in fact a standard 6.00mm t/e circuit is ok up to 15kW (subject to reference method, cable not surrounded by insulation etc)
 27 September 2012 09:00 AM
Probably more sensible to think of the "seperates" being a single "cooker"
At 240V, that would give a demand after diversity of about 20A - well within the capacity of a 6.0mm2 T&E
As Dave points out, even with a S/O, you could quite happily put a 15kW cooker on a 6.0mm2 cable with 30/32A protection (in a domestic setting)
 27 September 2012 09:13 AM
Jaymack
Should be OK, the maker usually gives recommendations on the kW loading etc., I use a 45A, easyfit, dual outlet plate as made by Click, their "Polar Accessories" - PRW 217.
 27 September 2012 09:07 PM
antric2
I may be incorrect here,but, I dont think induction hobs are allowed a diversified load.They have to be rated at full load.Check with the manufacturer or if you are registered,check with your scheme help line.
I will try to find where I read about induction hobs and full load.
Them Click dual boxes that Jaymack mentions are absolutely spot on and well recommended.
Antric
 27 September 2012 10:50 PM
GJH
Thanks for the replies, much appreciated guys. Will check out the dual boxes, cheers
 02 October 2012 07:31 PM
OldSparky
anyway the fuse will only trip, so the cable should be ok