Hello All,
Never come across this before so advice please.
Checked bonding done by shower installer couple of months ago before I started my work.1 length of 10mm to internal water stop tap and then unbroken loop to( or so I thought) to external gas box.I disconnected at met end and got excellent conti reading to the gas meter.
Did the job and by chance I went back to the job yesterday just to collect a tool and noticed that the gas was bonded to a 5mm piece of metal rod stuck in the ground.I hadnt seen this before because there was building rubbish covering all that area and the 10mm looked like it was going into the house so presumed wrong.
I will have to go back and run a 10mm now to bond the gas direct but why was the gas bonded to a rod in this way and seperate.
The good continuity comes from the cross bond at the boiler.
Good job I saw this as I am due NIC assessment and this is one of the jobs I might have used.
Regards
Antric
 31 August 2012 01:05 PM
User is offline View Users Profile Print this message



Ricicle

Posts: 829
Joined: 23 October 2006

I have seen a guy in a wholesalers once who was told by his 'plumber' that the gas wasn't bonded. He was in there buying an earth rod so he could 'earth the gas'. Don't know whether he had been told to do it this way or had decided himself.
Needless to say I had to have a little word !

-------------------------
Empty barrels make the most noise.
 31 August 2012 01:14 PM
User is online View Users Profile Print this message



daveparry1

Posts: 5896
Joined: 04 July 2007

I came across this recently when a gas "engineer" went to a property where I had done some work (which included gas and water bonding) to do a check of some kind or another and told the client that the gas pipe had to be connected to an earth rod whithin 600mm of the meter!

Dave.
 31 August 2012 01:27 PM
User is offline View Users Profile Print this message



antric2

Posts: 1034
Joined: 20 October 2006

Even after all these years I still havnt learned to stop presuming things...Doh!!
It would have been straight to re assessment visit if I hadnt seen it by this chance visit, so again lesson taken!
But it proves point again really that visual inspection and testing are a must together.
Antric
 31 August 2012 04:29 PM
User is offline View Users Profile Print this message


Avatar for weirdbeard.
weirdbeard

Posts: 1381
Joined: 26 September 2011

Originally posted by: antric2



Checked bonding done by shower installer couple of months ago before I started my work.1 length of 10mm to internal water stop tap and then unbroken loop to( or so I thought) to external gas box.




Just out of interest, where did the unbroken loop from the MET go to after it left the water stop tap?
 31 August 2012 06:11 PM
User is offline View Users Profile Print this message



baldelectrician

Posts: 311
Joined: 11 June 2005

Originally posted by: daveparry1

I came across this recently when a gas "engineer" went to a property where I had done some work (which included gas and water bonding) to do a check of some kind or another and told the client that the gas pipe had to be connected to an earth rod whithin 600mm of the meter!



Dave.


You must realise that all gas engineers are gods and always correct (even when they are usually wrong with electrics)

Mere mortal sparks look in awe and wonder at such knowlege

-------------------------
baldelectrician.com
 31 August 2012 08:15 PM
User is offline View Users Profile Print this message


Avatar for KFH.
KFH

Posts: 199
Joined: 06 November 2010

I was surprised to find exactly the same on a TT installation. The customer had put in an earth mat when building an extension as he had been told the ground locally was a poor earth. Ze of 15 Ohm. The Gas was bonded to a twig stuck in next to the meter so no idea how high its Ra will be, he thinks it was put in when the gas supply was installed. Have quoted for fixing it but have not heard yet. I assume the lack of any earth terminal in the electricity meter cabinet (next to the gas meter) confused the gas engineer.
 31 August 2012 09:15 PM
User is offline View Users Profile Print this message



peteTLM

Posts: 3085
Joined: 31 March 2005

Ive seen a few like this. Even worse, they were correctly done back to the met at the house and then had a rod outside.

All the plumbers think of is EARTH. They dont realise anything about potential difference......

-------------------------
----------------------------------------
Lack of planning on your part doesn't make it an emergency on mine....

Every man has to know his limitations- Dirty Harry
 31 August 2012 10:27 PM
User is offline View Users Profile Print this message



antric2

Posts: 1034
Joined: 20 October 2006

Originally posted by: weirdbeard

Originally posted by: antric2







Checked bonding done by shower installer couple of months ago before I started my work.1 length of 10mm to internal water stop tap and then unbroken loop to( or so I thought) to external gas box.









Just out of interest, where did the unbroken loop from the MET go to after it left the water stop tap?


Good question Weirdbeard!
Because I did conti test from MET end, disconnected, to gas pipe, I initially thought it was a straight run.Where the looped part from the stoptap goes is anybodies guess.I am going to have to go under the floor to feed 10mm to gas meter so will try to find where it is.
The continuity has been there because of the crossbonded boiler but this would have been a definite eyebrow raiser from my NIC assessor because even though I tested correctly, I would have given false understanding of the bonding because I had made a presumption about one end of the gas 10mm

In future, I am going to disconnect both ends of a 10mm bond.
Regards
Antric
 01 September 2012 08:55 PM
User is offline View Users Profile Print this message



GJH

Posts: 495
Joined: 24 January 2008

I bet the plumber charged the customer £300 for the privelage!

Bet they didn't query it either!