Good evening all.
I'm pricing a job to move the consumer unit location to a different part of the house to the meter. Switched fuse at meter position- swa- consumer unit. Am i correct in thinking that the ccc values would be the same as for pvc seeing as the connected accessories will be rated at 70Deg? ie. i will still need to use 25mm on a 100A fuse.

Thanks
 23 August 2012 06:58 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17567
Joined: 23 March 2004

Yup - treat it as PVC for what you are planning - Table 4D4A Column 2 gives you 118A for a 25mm2 x 2(probably 3) core

Regards

OMS

-------------------------
Failure is always an option
 23 August 2012 07:23 PM
User is offline View Users Profile Print this message



baronvoncaravan

Posts: 30
Joined: 06 September 2010

Thanks OMS, as i thought- that extra 11Amps will need to be paid for :-)
 31 August 2012 07:54 PM
User is offline View Users Profile Print this message


Avatar for weirdbeard.
weirdbeard

Posts: 860
Joined: 26 September 2011

Sorry if this is a bit late but I believe the BS standard for pvc/pvc/swa has been withdrawn and won't be replaced and apart from old stock all SWA cables now sold will be XPLE - this will no doubt be one of the future selling points of the next full edition of the regs book.
 31 August 2012 08:41 PM
User is offline View Users Profile Print this message



bpelectric

Posts: 3
Joined: 16 December 2008

If you go to eland co uk you can down load a free pdf doc with table 4E4A and table 4E4B .....90C XLPE / PVC /SWA / PVC . Depening on cost it might be worth useing XLPE as 25m twin will carry 146 Amps
 04 September 2012 10:43 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

Originally posted by: bpelectric

Depending on cost it might be worth using XLPE as 25m twin will carry 146 Amps


@90 degrees, which is higher than the limit for most devices......

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best