Good evening all.
I'm pricing a job to move the consumer unit location to a different part of the house to the meter. Switched fuse at meter position- swa- consumer unit. Am i correct in thinking that the ccc values would be the same as for pvc seeing as the connected accessories will be rated at 70Deg? ie. i will still need to use 25mm on a 100A fuse. Thanks |
|
|
|
|
|
|
|
|
Yup - treat it as PVC for what you are planning - Table 4D4A Column 2 gives you 118A for a 25mm2 x 2(probably 3) core
Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Thanks OMS, as i thought- that extra 11Amps will need to be paid for :-)
|
|
|
|
|
|
|
|
|
Sorry if this is a bit late but I believe the BS standard for pvc/pvc/swa has been withdrawn and won't be replaced and apart from old stock all SWA cables now sold will be XPLE - this will no doubt be one of the future selling points of the next full edition of the regs book.
|
|
|
|
|
|
|
|
|
If you go to eland co uk you can down load a free pdf doc with table 4E4A and table 4E4B .....90C XLPE / PVC /SWA / PVC . Depening on cost it might be worth useing XLPE as 25m twin will carry 146 Amps
|
|
|
|
|
|
|
|
|
Depending on cost it might be worth using XLPE as 25m twin will carry 146 Amps @90 degrees, which is higher than the limit for most devices...... ------------------------- Regards Martyn. Only a mediocre person is always at their best www.electrical contractors uk.com |
|
|
|
|
|