Topic Title: boiler swap and supplementary bonding
Topic Summary: whats required
Created On: 16 August 2012 02:32 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 16 August 2012 02:32 PM
User is offline View Users Profile Print this message



bigbazsparky

Posts: 32
Joined: 05 July 2007

good afternoon guys and gals.
when an heating engineer swaps just the combi boiler in a domestic property what actually is the requirements for supplementary bonding of the boiler and does the bathroom pipework rad etc still need to be bonded if the existing install isnt upto 17th edition?
 16 August 2012 02:53 PM
User is online View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17599
Joined: 23 March 2004

Originally posted by: bigbazsparky

good afternoon guys and gals.

when an heating engineer swaps just the combi boiler in a domestic property what actually is the requirements for supplementary bonding of the boiler


None really - you would expect adequate continuity through the gas and CWS to the LTHW and HWS. There is a small risk that you lose continuity through any F&E tank that may be fitted - but equally, that should also isolate the downstream pipework from being extraneous

and does the bathroom pipework rad etc still need to be bonded if the existing install isnt upto 17th edition?

Well, bonding (as the 16th edition) is still required if all circuits of the location are not RCD proteced and you cannot verify the adequacy of main bonding see 701.415.2

Although, like all these things BS 7671 isn't retrospective. If there is no supplementary bonding, then probably worthy of a comment if there is also no RCD protection



Regards

OMS

-------------------------
Failure is always an option