Topic Title: Shower install
Topic Summary: Routing cable
Created On: 04 August 2012 12:10 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 04 August 2012 12:10 PM
User is offline View Users Profile Print this message



ELIP

Posts: 63
Joined: 18 November 2007

I have been asked to have a look at proposed shower install. The bathroom is downstairs in a flat roofed single story extension. The only way to route the cable is to go outside onto the exterior wall. The run is approx 20m then drill back into the house for the shower switch.
I need to decide whether to use swa or plastic conduit.

Just had a look in App 3 at 4mm 90 degrees thermosetting swa is good for 49A. Having read the note it says that the switchgear etc must be suitably rating for the same temperature.

Can anyone advise on the easiest way to do this. I was surpised that 4mm seems to be adequate.....have I missed something?

Thanks.
 04 August 2012 12:33 PM
User is offline View Users Profile Print this message



alanblaby

Posts: 394
Joined: 09 March 2012

The higher temperature rating of the 90 deg. cable allows it to pass more current. If it was limited to 70 degrees max, then the rated current for it would be lower.
Why SWA?
T+E, in trunking if need be,or covered in capping, would be far easier. 6mm may suffice, I'd be tempted to go for 10mm T+E anyway, as showers are only going top get more powerful - there were no 10.8kW showers a few years ago, now they are common, and the difference in price between 6 and 10mm is pretty small as an overall cost of fitting the shower.
 04 August 2012 12:40 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3532
Joined: 17 December 2004

As has been pointed out to me recently, 90deg thermosetting cables are only good for that rating if the corresponding switchgear is also rated for the same temperature. So it might be wise to use table 4D4A and upgrade the cable to 6 or 10mm2.

It gets worst with 4D1A and you would have to go with 10mm2 in 25mm2 conduit.

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 04 August 2012 12:51 PM
User is offline View Users Profile Print this message



MrP

Posts: 847
Joined: 24 March 2006

Plastic capping run on an external wall come on life can't possibly be that bad
If it's got to be external personally I'd galv tube it with appropriately sized cable for the load not for a future load that might or might not get used

MrP
plastic capping on an external wall what is the world comimg too
 04 August 2012 01:07 PM
User is offline View Users Profile Print this message



MPVaughan

Posts: 106
Joined: 07 August 2010

LOL, you galv tube it mate and let every man and his dog undercut you! Are you self employed?



Originally posted by: MrP

Plastic capping run on an external wall come on life can't possibly be that bad

If it's got to be external personally I'd galv tube it with appropriately sized cable for the load not for a future load that might or might not get used



MrP

plastic capping on an external wall what is the world comimg too
 04 August 2012 01:50 PM
User is offline View Users Profile Print this message



MrP

Posts: 847
Joined: 24 March 2006

Think you will find galv tube cheaper than plastic a better engineering solution less chance of a call back wont warp looks better wins in my books
Or would you go for the plastic capping
MrP
We all work for ourselves
 04 August 2012 02:02 PM
User is offline View Users Profile Print this message



DOUGIE1000

Posts: 4176
Joined: 13 August 2005

Plastic capping exterior, haha

-------------------------
Dougie
Power Plus Electrical.co.uk

My mission is to live as long as possible......so far so good!
 04 August 2012 02:20 PM
User is offline View Users Profile Print this message



MPVaughan

Posts: 106
Joined: 07 August 2010

Stock + die, cutting compound, end boxes, saddles, couplers, singles, labour etc etc

You wont win the job, its a domestic shower not a plant room!
 04 August 2012 02:32 PM
User is offline View Users Profile Print this message



ELIP

Posts: 63
Joined: 18 November 2007

Originally posted by: Legh

As has been pointed out to me recently, 90deg thermosetting cables are only good for that rating if the corresponding switchgear is also rated for the same temperature. So it might be wise to use table 4D4A and upgrade the cable to 6 or 10mm2.
It gets worst with 4D1A and you would have to go with 10mm2 in 25mm2 conduit.

Legh


Thanks Legh, looks like doing it in 6mm swa then. I was a bit unsure with the 90 degree thermosetting. Is the cable likely to get that hot with approx 40A flowing. If it doesn't get anywhere near that hot does it really matter if the switch gear is only rated at 70 degrees?
 04 August 2012 02:50 PM
User is offline View Users Profile Print this message



Fm

Posts: 741
Joined: 24 August 2011

Whats the Ground floor construction of the house amd extension?
 04 August 2012 02:53 PM
User is offline View Users Profile Print this message



MrP

Posts: 847
Joined: 24 March 2006

Originally posted by: MPVaughan

Stock + die, cutting compound, end boxes, saddles, couplers, singles, labour etc etc



You wont win the job, its a domestic shower not a plant room!


As a electrician you would carry this stuff in your van wouldn't you?
You still have to buy the bits in plastic and as crazy as it sounds s galv is cheaper than PVC
Plus a better engineering solution

You will never compete against bodgit and scarper who run the cable incased by capping

MrP
 04 August 2012 03:09 PM
User is offline View Users Profile Print this message



MPVaughan

Posts: 106
Joined: 07 August 2010

Just because its in my van, doesnt mean the client gets it for free!

Im not saying be rough, win the job by discussing options with the client.
If another guy prices to clip direct youve got no chance, another days work gone and the cupboards are already bare...

Quote;
As a electrician you would carry this stuff in your van wouldn't you?

You still have to buy the bits in plastic and as crazy as it sounds s galv is cheaper than PVC

Plus a better engineering solution



You will never compete against bodgit and scarper who run the cable incased by capping



MrP
 04 August 2012 03:42 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3532
Joined: 17 December 2004

Originally posted by: ELIP

Originally posted by: Legh

As has been pointed out to me recently, 90deg thermosetting cables are only good for that rating if the corresponding switchgear is also rated for the same temperature. So it might be wise to use table 4D4A and upgrade the cable to 6 or 10mm2.

It gets worst with 4D1A and you would have to go with 10mm2 in 25mm2 conduit.

Legh


Thanks Legh, looks like doing it in 6mm swa then. I was a bit unsure with the 90 degree thermosetting. Is the cable likely to get that hot with approx 40A flowing. If it doesn't get anywhere near that hot does it really matter if the switch gear is only rated at 70 degrees?


As I see it. Its as much for fault conditions as its for normal running temperature. The assumed starting temperature at the time of the fault would be taken as 70deg rising to its maximum of 160deg. If the cable is running normally at a lower temperature then you have some leeway and protection against overheating. As well as the current and time limiting affect of the protective device.

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 04 August 2012 09:31 PM
User is offline View Users Profile Print this message


Avatar for Rulland.
Rulland

Posts: 477
Joined: 11 April 2008

Trunking, capping or 25mm metal conduit!.........
Capping surely?, trunking and capping allow an easier run, conduit with 10mm in boxes etc=nightmare, capping my bet tbh.

-------------------------
Those who make no mistakes do very little work!!......
 04 August 2012 09:55 PM
User is offline View Users Profile Print this message



Fm

Posts: 741
Joined: 24 August 2011

Could you run swa external, and convert to t and e on the inside.

I think capping outside would look rough.
 05 August 2012 10:56 AM
User is offline View Users Profile Print this message



ELIP

Posts: 63
Joined: 18 November 2007

Originally posted by: Fm

Could you run swa external, and convert to t and e on the inside.

I think capping outside would look rough.


Its going to be SWA all the way. Drill through wall from meter cupboard, 20mm galv end box on outside wall, SWA vertical to high level, then horizontal for 20m, drop down to height of shower switch, another galv end box, then through the wall for the switch.

Can't believe people would seriously consider doing this in capped T/E