Topic Title: RCD socket tripping
Created On: 03 August 2012 04:33 PM
cesltd
Installed an RCD socket for a customer who needed it for a new fridge freezer. Fully tested the RCD, times fine, ramp test came up at 29mA. Customer called to say the RCD keeps tripping.
Advised her that the new Beko fridge freezer must be faulty. The fridge has been replaced but the tripping is still happenning. Any ideas? Two faulty fridges in a row seems a bit unlikely.
 03 August 2012 06:52 PM
jumpinjax
Can i ask why an RCD socket was installed and if there was any leakage between live and earth conductors?
 03 August 2012 07:01 PM
cesltd
I installed the RCD socket as there were no RCDs in the board and I was able to spur off the downstairs ring using surface trunking. No leakage between live and earth conductors.
 03 August 2012 07:14 PM
Avatar for dg66.
dg66
Friges and freezers are not the best appliances to have on RCD protected circuits,if all the new wiring is surface then no RCD required for that and if the socket is dedicated for the fridge freezer,why not put a fused connection unit in?
Dave(not Cockburn)
 03 August 2012 09:39 PM
cesltd
I did think about an FCU, but then cutting the plug off could be problematic if she needs a warranty repair? She asked for a twin socket, so maybe I'll replace the RCD twin socket with a single socket and label it for Fridge use only.
 03 August 2012 09:51 PM
That would be the best thing to do i'd say! Also check that you have wired the socket correctly,
 04 August 2012 12:44 AM
It would be worth a quick check on the fridge too. We came across one a while ago that had a neutral - earth cross in the moulded plug of the mains cable fitted in the factory! I don't recall the make after all this time.
 05 August 2012 05:00 PM
I have had both my fridge and freezer on a single 30mA RCD in my last three houses (total about 20 years) and never had either of them responsivle for a trip.
As before, check the circuit is wired properly, and check that the earth pin on the fridge's mains lead is actually connected to the earth terminal on the fridge!
 05 August 2012 05:33 PM
Avatar for Rulland.
Rulland
The op has said two fridges have manifested the same fault-unlikely to be the fridge, must be something to do with the circuit I reckon.
 05 August 2012 06:08 PM
Avatar for ebee.
I`d be tempted to try a few more appliances (assuming you`ve done all the metered tests) .
It`s either a faulty RCD socket (but if you`ve tested that is less likely) or its the fridge(s) or its a poor connection to the RCD socket and its the active (or do I mean passive?) type so with power loss it becomes unenergised and stays that way.
 06 August 2012 01:27 PM
grahamstyles
Just a thought, I was called to an office where the SRCD was tripping now and then and it was found to be a mobile phone that was being charged from the socket,when it was being charged the phone was resting on top of the socket and when the phone was called the SRCD tripped. The small handshake that was transmitted when the phone was called was inducing a current into the coil of the SRCD and tripping it. Luckily I was there when the phone rang or I would have been searching forever.