 04 October 2012 09:44 PM
User is offline View Users Profile Print this message


Where is my avatar image?
weirdbeard

Posts: 1901
Joined: 26 September 2011

Originally posted by: AJJewsbury



I've been thinking again about this one. 705.411.1 (by the numbering) is modification to the requirements of section 411 - i.e. ADS.

.


Must admit that although i've worked on farms in the past for employers, it's only fairly recent that i've had to get stuck into the regs concerning these - just having a quick look at the 16th and the system in that seems a bit more common sense - ie where the special location requires something different to the standard regs it often says reg xxx-xx-xx is relaced by reg 605-xx-xx.

-------------------------
: - )
 04 October 2012 10:45 PM
User is offline View Users Profile Print this message


Where is my avatar image?
OldSparky

Posts: 600
Joined: 28 June 2011

if you think about it all tails on a TT supplies are un protected...
 05 October 2012 10:18 AM
User is offline View Users Profile Print this message


Where is my avatar image?
AJJewsbury

Posts: 12526
Joined: 13 August 2003

if you think about it all tails on a TT supplies are un protected...

Not protected by ADS, but hopefully protected by double or reinforced insulation or equivalent.
- Andy.
 07 October 2012 07:39 PM
User is offline View Users Profile Print this message


Where is my avatar image?
weirdbeard

Posts: 1901
Joined: 26 September 2011

Originally posted by: slittle




Bear in mind you won't get a PME connection anyway so you've got to TT it and the first protective device on a TT has to be an RCD.



From a description by the owner, it sounds like it's going to be TN-S, he says theres a separate earth cable been run between the intake and the transformer, that has been staked at several points in the trench, though I've yet to confirm this with the authoroties.

-------------------------
: - )