Today we have dug out new trenches ready for redirected a 11KV cable. We are only rerouting half of the cable, so we started at one end and made our way to where the joint was going to made off.
When we were digging out the existing cable we hit a concrete bed. This concrete bed was covering the existing cable, with a width of about 1 Metre.
Out of curiosity and confusion, we unearthed the cable at several locations and found that cable was covered with concrete there too.
Has anybody else experienced this kind of protection over a buried cable?

Note: - the cable is at least 30 years old, maybe 40

-------------------------
Fail to prepare...Prepare to fail!

Adam
 20 July 2012 03:09 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17743
Joined: 23 March 2004

Not uncommon - a lean mix dropped into the trench after stonedust or sand partial backfill was a quick and cheap method of providing what in this case is a continuous cable "tile".

concrete was a specification requirement in some arenas for protection against digging, sometimes as a protection against terrorism and sometimes just becasue that's what the electrical engineer always did

regards

OMS

-------------------------
Failure is always an option
 20 July 2012 03:24 PM
User is offline View Users Profile Print this message



adamtaylor

Posts: 44
Joined: 08 December 2009

So from your experience,

What would you estimate the depth of this concreate?

Or is this a stupid question???

-------------------------
Fail to prepare...Prepare to fail!

Adam
 20 July 2012 03:45 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17743
Joined: 23 March 2004

Normally 4" of 1:3:9 of OPC, sand and aggregate (ie a lean mix) - but it could be anything at that age - I've seen it with 200mm+ of gen 2 mix and reinforcing mesh in before - just because they had some "spare"

Good luck - breaking out concrete around cables if it isn't on proper bedding is a right bitch

regards

OMS

-------------------------
Failure is always an option
 21 July 2012 12:43 AM
User is offline View Users Profile Print this message



alancapon

Posts: 5524
Joined: 27 December 2005

It would be interesting to read your risk assessment. Assuming that the cable is still live, digging through concrete towards a known 11kV cable is a high risk scenario if you don't know the depth of the concrete or the depth of the cable! The safest option is to isolate it while the cable depth / concrete depth is determined. The safe option is to leave the cable off until the concrete has been removed.

Regards,

Alan.
 21 July 2012 02:05 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3109
Joined: 22 November 2007

Alan,

The other option could be to get someone to hit it with a digger and the resulting blast may clear the concrete if the protection doesn't operate fast enough.

Can't see the RAMS beginning signed off for it though


Stu
 21 July 2012 04:42 PM
User is offline View Users Profile Print this message



simongallagher

Posts: 148
Joined: 28 July 2005

The cable can be made dead to remove the concrete, or dig down away from the cable, then undermine the concrete (assuming the cable is not encased all the way around).

Simon
 22 July 2012 08:55 PM
User is offline View Users Profile Print this message


Avatar for Dave69.
Dave69

Posts: 416
Joined: 16 July 2011

Originally posted by: slittle

Alan,



The other option could be to get someone to hit it with a digger and the resulting blast may clear the concrete if the protection doesn't operate fast enough.



Can't see the RAMS beginning signed off for it though





Stu


I'm sure there are plenty of digger drivers that will give it a go if there's an offer of free fish and chips or if you just tell him you have to find the cable asap and its "job and knock"

Just make sure the RAMS mention wearing ear muffs
 24 July 2012 07:53 AM
User is offline View Users Profile Print this message



adamtaylor

Posts: 44
Joined: 08 December 2009

Originally posted by: alancapon

It would be interesting to read your risk assessment. Assuming that the cable is still live, digging through concrete towards a known 11kV cable is a high risk scenario if you don't know the depth of the concrete or the depth of the cable! The safest option is to isolate it while the cable depth / concrete depth is determined. The safe option is to leave the cable off until the concrete has been removed.



Regards,



Alan.


Hi Alan,

I wouldn't even entertain the idea of keeping the cable live, whilst trying to uncover the the concrete pad.

This job will now be done in the next shut down and removed once all power is off.

-------------------------
Fail to prepare...Prepare to fail!

Adam
 24 July 2012 07:55 AM
User is offline View Users Profile Print this message



adamtaylor

Posts: 44
Joined: 08 December 2009

Originally posted by: OMS

Normally 4" of 1:3:9 of OPC, sand and aggregate (ie a lean mix) - but it could be anything at that age - I've seen it with 200mm+ of gen 2 mix and reinforcing mesh in before - just because they had some "spare"



Good luck - breaking out concrete around cables if it isn't on proper bedding is a right bitch



regards



OMS


Sounds like we have an intresting task infront of us then,

I will let you know the results of the depth, once discovered

-------------------------
Fail to prepare...Prepare to fail!

Adam