Topic Title: Existing Main Bonding - Definition of 'Adequate'
Topic Summary:
Created On: 08 July 2012 12:00 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 08 July 2012 12:00 PM
User is offline View Users Profile Print this message



Richard64

Posts: 205
Joined: 15 October 2009

Reg 132.16
Scenario.
Two bonds to Gas. One disconnected.
The other run back to a local DB not the MET.
Would this second bond be considered adequate, although strictly speaking non compliant?
 08 July 2012 01:18 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

Is there a connection between the CU earth bar and the MET?
If yes, then it complies. Assuming the connecting conductor is sized appropriately.
If no, then not only does it not comply, but it is not adequate.