Could anybody recommend a product that would meet the requirements to seal conduit ends within an ATEX zone 2 environment. I have been involved in industries with ATEX equipment/zones for a number of years. However I have never had to seal conduit runs within zoned areas. I have done a bit of research and can't really find anything that is used. Having spoken to some contractors they have used a resin, blocked the conduit poured to resin in to set. They could not confirm if what they used was certified. However I'm not sure if there is a product of this type that is.

Could anybody help me if they know if a product (it's name) that can be used and where to get it from, a wholesaler, RS etc.

Your help will be very much appreciated.

Kind regards,

Mark.
 04 July 2012 11:36 AM
User is offline View Users Profile Print this message


Avatar for rocknroll.
rocknroll

Posts: 8878
Joined: 03 October 2005

Been a long time but there are a number of certified resins specifically designed for this purpose and they all came out of the '3M Scotchcast' stable and generally available, they came in numbers and I think number 4 is probably the specification you might require but enquiry would be needed..

Should be available through larger electrical wholesalers.

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------

Edited: 04 July 2012 at 11:48 AM by rocknroll
 04 July 2012 11:44 AM
User is offline View Users Profile Print this message


Avatar for neilparsons.
neilparsons

Posts: 31
Joined: 29 October 2002

You need a compound filled stopper box to seal the ends of the conduit, try Peppers or Raxton. You may struggle to get them off the shelf at most wholesalers, not as many people install conduit in hazardous areas these days.
 04 July 2012 12:22 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19747
Joined: 23 March 2004

I agree, for conduit and cables you need a conduit compound filled stopper box - you may also need to check the cable stranding/filling isn't providing a gas path and the cable outer can be effectively sealed.

Just putting resin in the conduit isn't likely to be acceptable

regards

OMS

-------------------------
Failure is always an option
 04 July 2012 04:39 PM
User is offline View Users Profile Print this message



Fm

Posts: 710
Joined: 24 August 2011

google rise sealing kits
 05 July 2012 03:15 PM
User is offline View Users Profile Print this message



markthemariner

Posts: 11
Joined: 14 May 2010

Cheers fellas.

Your advice and suggestions has been excellent. I agree I would stay well away from conduit in an ATEX envrionment. This is the first instance in 20 years I have seen it that needed to be dealt with.

I did manage to get in touch with someone from 3M Scotchguard. They do a resin that meets all the requirements that are needed for the job in question. They even sent me electronic documentation that confirms the resin is suitable for an ATEX environment.

I did check out the rise seal kits as well, an excellent product that I will be keeping a note of for the future. I can see me using this a lot in the job I am in currently.

Thanks again. There is some great advice and expertise on this forum and within the IET.
 06 July 2012 01:04 AM
User is offline View Users Profile Print this message



stableford

Posts: 64
Joined: 04 April 2006

Although not an ATEX enviroment, the north american Class, and Division system regularly uses conduit. In Alberta its part of the additional petrochemical regs to the wiring code to install double seals.
1 being the seal on the device, the other being an inline conduit seal.
Poured in and permanent.