Topic Title: 53A hydraulic pump on 63A fuse. Topic Summary: Created On: 03 July 2012 07:44 PM Status: Post and Reply |
A customer requires a new supply for a 30kw hydraulic test pump motor,(star delta)All existing dis boards use obsolete Dorman Smith mcb,s & main busbars cannot be isolated.There,s a spare 63A BS88 switch fuse available & I wondered if it was worth trying this before trying to find another solution.Thanks for any advice,
hz |
Swap the fuses for gM pattern, say 63/100 (if the EFLI will permit)
Regards OMS ------------------------- Failure is always an option |
With a 30kW motor you are getting towards the upper limit for a star/delta start on 63A BS88 fuses. As OMS said, your best bet would be 63A motor rated fuses. I would suggest 63M80.
Thanx for the help,will try fuses as suggested.
Regards,hz. |
The Power pack should start unloaded and should be able to start with a minimal start time and current, the 63A switchfuse if AC3 should be fine if the power pack and the fluid circuts are designed properly.
------------------------- James |
Hi,