 02 July 2012 10:12 AM
User is offline View Users Profile Print this message



SKElectrical

Posts: 697
Joined: 01 February 2009

Domestic customer called this weekend... and said that the company who he has bought a cooker from, has told him that the cooker should not be installed with rcd protection as it will continuously trip. It seems odd to me and i havent heard of this before, has anyone else?
 02 July 2012 10:20 AM
User is offline View Users Profile Print this message



aligarjon

Posts: 2439
Joined: 09 September 2005

It can be a big problem with some of these large beasts. i had one in a new build a few years ago, luckily they told me at first fix stage so i wired it in SWA. A pain in the bum on an existing circuit. It will probably need a new circuit, or dig the buried cable out, i wouldn't want to be the one to take it off an existing rcd. Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 02 July 2012 11:31 AM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9765
Joined: 13 August 2003

I doubt they really mean no RCD at all - it would make it impossible to install on TT systems - which would knock a large hole in the EU market. Maybe the leakage is too much for a 30mA RCD... perhaps.

If the leakage really is that high you'd be well into section 543.7 (high protective conductor currents) territory - so beware of T&E with small c.p.c.s.

- Andy.
 02 July 2012 01:16 PM
User is offline View Users Profile Print this message



mikejumper

Posts: 1548
Joined: 14 December 2006

Originally posted by: SKElectrical
Domestic customer called this weekend... and said that the company who he has bought a cooker from, has told him that the cooker should not be installed with rcd protection as it will continuously trip. It seems odd to me and i havent heard of this before, has anyone else?

No.
It may be the retailer saying this rather than the manufacturer.
 02 July 2012 08:51 PM
User is offline View Users Profile Print this message



GB

Posts: 316
Joined: 04 September 2002

Sounds like a strange one! do you think they mean high leakage currents or if not cleaned / maintained they can cause problems.
It would be worth looking at the manufacturers instructions to see what is mentioned, maybe the people in the shop are at the end of a chinese wisper!!
 03 July 2012 07:39 PM
User is offline View Users Profile Print this message



DOUGIE1000

Posts: 3975
Joined: 13 August 2005

Installing a cooker on an rcd isn't a problem, however old elements can cause problems when cooker old. No a problem a cooker on rcd.

-------------------------
Dougie
Power Plus Electrical.co.uk

My mission is to live as long as possible......so far so good!
 03 July 2012 07:52 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

Cooker elements often referred to as 'black iron' elements, absorb moisture from the atmosphere.
If they are not used for some time, they will cause RCDs to trip.
Brand spanking new cookers are as prone to this as old cookers.
The greater the length of time between manufacture and first utilisation, the greater the chance they will cause the RCD to trip