TT. Just run an SWA sub main to an annexe. Split the tails into an insulated enclosure, 100mA RCD-S and then, at great expense, a Merlin 80A double pole MCB as I have it in my head that double pole is required for TT. However, I can't find a reference to it in the BGB. Any pointers or am I barking? Thanks. Woof!
|
|
|
|
|
|
|
|
|
537.2.2.1 "A device for isolation shall isolate all live supply conductors from the circuit concerned, subject to the provisions of Regulation 537.1.2."
|
|
|
|
|
|
|
|
|
TT. Just run an SWA sub main to an annexe. Split the tails into an insulated enclosure, 100mA RCD-S and then, at great expense, a Merlin 80A double pole MCB as I have it in my head that double pole is required for TT. However, I can't find a reference to it in the BGB. Any pointers or am I barking? Thanks. Woof! Not barking - just that you could have relied on the slugged RCD for isolation (as it is double pole) and used a single pole MCB for overload and short circuit protection Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Depends whether the MCB is intended to provide isolation.
|
|
|
|
|
|
|
|
|
Well if the MCB is intended to provide isolation in addition to the RCD (sort of double blocking) then yes it will need to be double pole
For compliance with BS 7671 it doesn't need to be though - the RCD can perform that function - as could any double pole switch essentially - including the installation main switch, which by virtue of this 9probably being domesytic or similar) needs to be double pole regardless of earthing type. Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
So to work on one circuit in a TT installation the whole installation would need to be turned off if all you had were single pole rcbo's and a double pole main switch?
|
|
|
|
|
|
|
|
|
Thanks for your replies. Who wants to make a profit anyway!
|
|
|
|
|
|
|
|
|
That's about the strength of it Typiod but it would comply,
Dave. |
|
|
|
|
|
|
|
|
The MCB may not be a good idea on discrimination grounds either! Old fashioned BS88s are a better bet.
------------------------- David CEng etc, don't ask, its a result not a question! |
|
|
|
|
|
|
|
|
So to work on one circuit in a TT installation the whole installation would need to be turned off if all you had were single pole rcbo's and a double pole main switch? Effectively yes - but resilience and operational durability aren't really considerations of BS 7671 are they. i was simply pointing out that there should be DP isolation - if that is a single device at the origin or multiple devices controlling individual or smaller groups of circuits then that's a case of engineering judgement. In practice, wouldn't most sparks isolate the submain in the OP by just popping the RCD test button ? (and probably giving the RCD to only exercise it ever gets - regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
OMS - if only we lived in Electrical Utopia!
|
|
|
|
|
|
|
|
|
LoL- then we'd have a double pole RCD and a double pole MCB for double blocking isolation of the sub main - in a domestic - utopia indeed -
Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
But would we earth heating radiators with plastic pipes????
|
|
|
|
|
|
|
|
|
Well I guess you or I wouldn't - I can think of one guy who just might though !!
OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Which came first the chicken or the egg?
Or in this case the RCD or the MCB? Does it matter? Andy |
|
|
|
|
|
|
|
|
The Egg of course! Simples
------------------------- Regards, Ebee (M I S P N) Knotted cables cause Lumpy Lektrik |
|
|
|
|
|
|
|
|
Or in this case the RCD or the MCB? Does it matter? Ideally have the DP RCD upstream of the SP MCB - if you get a N-PE fault simultaneously with or after a L-N fault, you want the RCD to trip to remove the N-PE fault (especially if you have more RCDs upstream) - but if the MCB trips first and is upstream of the RCD, the RCD will be deprived of power and so won't trip. OK, the chances are small and the consequences usually not dangerous, but ideally... - Andy. |
|
|
|
|
|