Topic Title: PIR / EICR advice on the following
Topic Summary:
Created On: 25 June 2012 05:25 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 25 June 2012 05:25 PM
User is offline View Users Profile Print this message



Smith249

Posts: 332
Joined: 09 September 2004

Carrying out an inspection in a factory, many things found wrong.

Few I'm not sure of.

1) SWA sub-main running for 30 meters is cable tied directly to a 50mm main gas pipe. What code would you give this? - the owner of the factory cannot see a problem with it.

2) The installation is TT Ra is 150ohms, there is no RCD anywhere, and it's all metal DBs and rusty old steel trunking. C2?

I think both code 2's but little unsure about the SWA

Thanks.


 25 June 2012 05:34 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17567
Joined: 23 March 2004

Both code 1,s I would have said

1 - if the gas main wasn't designed to support the swa load, you could have a sudden and immediate fracture - with the attendant outcome. BS 7671 warns against detrimental influence and proximity to non electrical services. The gas regulations would take a stiffer view.

2 - Ra = 150 ohms and no RCD - how is ADS being achieved then

OMS

-------------------------
Failure is always an option
 25 June 2012 06:38 PM
User is offline View Users Profile Print this message



Smith249

Posts: 332
Joined: 09 September 2004

Thanks for the reply,

The thing is the gas pipe is a heavy duty, threaded 50mm pipe, fixed with heavy duty brackets to the wall, I couldn't imagine the SWA is stressing it, wouldn't code 2 be more appropriate?

 25 June 2012 06:44 PM
User is offline View Users Profile Print this message



Fm

Posts: 391
Joined: 24 August 2011

Services should be independantly fixed from each other.
Regs is in the office, its there near the start!
 26 June 2012 07:46 PM
User is offline View Users Profile Print this message



Fm

Posts: 391
Joined: 24 August 2011

Whats your opinion on this, is this the same installation as the garage ramp?
 26 June 2012 08:48 PM
User is offline View Users Profile Print this message



GB

Posts: 316
Joined: 04 September 2002

Both code 1 & both dangerous
Gas pipes can not be used for anything else including cable support, its not unusual to find that the client does not think anything is wrong but his opinion does not realy count.
 26 June 2012 09:04 PM
User is offline View Users Profile Print this message


Avatar for KFH.
KFH

Posts: 169
Joined: 06 November 2010

I would have said that both are C2 - Potentially dangerous, urgent remedial action required. GN3 give an example of C2 as "non earthed installation as it requires a further fault to manifest injury". The lack of an RCD is only a problem in the event of a further fault.

C1 is risk of injury, immediate action required and gives examples such as badly damaged equipment with risk of access to live parts and bare live parts.
 27 June 2012 12:47 AM
User is offline View Users Profile Print this message


Avatar for davezawadi.
davezawadi

Posts: 2421
Joined: 26 June 2002

Again you should not be doing EICRs.

-------------------------
David
CEng etc, don't ask, its a result not a question!