Topic Title: running a 5kw instantaneous water heater on a 2.5mm
Topic Summary:
Created On: 25 June 2012 01:01 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 25 June 2012 01:01 PM
User is offline View Users Profile Print this message



aligarjon

Posts: 2458
Joined: 09 September 2005

looked at a little job today for a customer. he wants to remove his imersion tank located in the roof and fit 2 local instant heaters under sinks in cupboards in bathroom and kitchen. The imersion supply is switched in kitchen and goes via a spur outside the bathroom that used to feed a whirlpool bath (so both on same radial via a B16 breaker). he is happy to fit both heaters onto same radial, ive explained that he will only be able to use 1 at a time, and in reality thats all that will happen.
I was innitially looking at a couple of 3.5kw models(perfect 35), but after reading reviews etc would prefer the 5kw models. obviously this is pushing it a bit with the cable and the breaker. I could upgrade the breaker to a 20amp (2.5 cable) but still a bit tight.
On the other hand its an instant heater and will only run for a few seconds at a time so not really a problem even with the B16.

An opinions/advice would be appreciated.

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 25 June 2012 01:07 PM
User is offline View Users Profile Print this message



Ricicle

Posts: 803
Joined: 23 October 2006

Is the cable likely to suffer from overheating by it's install conditions if you were to put in a 20 or even 25A breaker (and the load running times) ?

-------------------------
Empty barrels make the most noise.
 25 June 2012 01:14 PM
User is offline View Users Profile Print this message



aligarjon

Posts: 2458
Joined: 09 September 2005

I don't think there will be a problem on the 16amp to be honest if i'm reading the curves right. It needs over 20amps before it even touches the 16amp curve, that with the fact that they will only run for a minute maximum so i see no problem with cable overheating. there is no insulation in the floors.

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 25 June 2012 01:22 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5337
Joined: 04 July 2007

I think i'd be happy with it Gary, after all the breaker will be protecting the cable, the worst that could happen is the breaker tripping, I think i'd go for a 20 amp breaker though,

Dave.
 25 June 2012 01:53 PM
User is offline View Users Profile Print this message


Avatar for weirdbeard.
weirdbeard

Posts: 861
Joined: 26 September 2011

Hi gary, the 5 kw instantaneous unit might be ok for hand washing use in the bathroom but I would seriously consider recommending a heater with a bit of storage for the kitchen for washing up etc, the instantaneous 5kw would take 5 minutes to fill a 10L bowl @50C

http://www.ascot-hygiene.co.uk/technical.html
 25 June 2012 02:01 PM
User is offline View Users Profile Print this message



aligarjon

Posts: 2458
Joined: 09 September 2005

Thanks guys. cheers for the link weirdbeard, thats really helpful.

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 25 June 2012 04:18 PM
User is offline View Users Profile Print this message



GB

Posts: 319
Joined: 04 September 2002

Dependent on the installation method the cable rating may be 18.5A so uprating the fuse may not be an option (cable type ?)
Also is VD an issue? 5kw on a 2.5mm may not be a long run before there are issues (30M ish)
 26 June 2012 12:24 AM
User is offline View Users Profile Print this message



stableford

Posts: 64
Joined: 04 April 2006

Forgive my ignorance- since I moved to Canada, has there been a change in the regs- I believe it used to be a max of 3kW fixed load on 2.5 - hence immersion ccts.
 26 June 2012 08:08 AM
User is offline View Users Profile Print this message



aligarjon

Posts: 2458
Joined: 09 September 2005

Originally posted by: GB

Dependent on the installation method the cable rating may be 18.5A so uprating the fuse may not be an option (cable type ?)

Also is VD an issue? 5kw on a 2.5mm may not be a long run before there are issues (30M ish)


its standard pvc/pvc . the run is 10m max .They had some building works done 15 years or so ago and the ceilings were down so he has told me and there is not any insulation in the ceiling. running in a new supply would cause a lot of disruption because of the directions of the joists and polished up old floorboards and a chimney breast. thats before navigating the kitchen

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 26 June 2012 08:48 AM
User is offline View Users Profile Print this message



GB

Posts: 319
Joined: 04 September 2002

As the design current is greater than 20A you would have to rate the breaker at (433.1.1) 25A
If we are saying the pvc/pvc is clipped direct with no insulation it could be rated at 27A but personally having not installed the cable etc etc I would install a new cable, to tight for my liking!!
I tend to draw a bit of a line at 3kW for 2.5mm
 26 June 2012 10:01 AM
User is offline View Users Profile Print this message


Avatar for BigRed.
BigRed

Posts: 517
Joined: 10 November 2006

you are the designer, how good is your indemnity insurance!. Ask yourself, if this was in your gaff, would you be happy with it?. In theory, pretty close. Practice? In reality, will only one be used? Will someone competent be there who knows the set up?
 26 June 2012 10:50 AM
User is offline View Users Profile Print this message



GB

Posts: 319
Joined: 04 September 2002

After re-read
2no 5kW heaters on one circuit? unless they cant be operated together you would have to asume they could (would) be operated together.
I would run two new circuits in and atleast you can sleep at night!!
 26 June 2012 11:29 AM
User is offline View Users Profile Print this message



daveparry1

Posts: 5337
Joined: 04 July 2007

Although I tend to agree with you GB, yes in an ideal world another circuit would be preferred or maybe replace the existing cable with 4.00mm or 6.00mm and fit a 32 amp breaker but in the real world it's not always practicable to do things the way we would like. At the end of the day the existing cable will be well protected by the 16a or 20a mcb, the worst that could happen is occasional tripping of the mcb, (also bear in mind that they are instantaneous heaters so will only be on for a few minutes at a time)

Dave.
 26 June 2012 11:47 AM
User is offline View Users Profile Print this message



GB

Posts: 319
Joined: 04 September 2002

If it were a perfect world I would not be in it....thats for sure!!>>>>
Although it is over to the designer you would have to say it would be very poor design and will only come back bite somebodies backside,
I would also tend to say the problem is not the sparks but the clients............ until you undertake the work.
Fuse would have to be sized at 25A to comply and not sure I would fancy that!!




 26 June 2012 11:48 AM
User is offline View Users Profile Print this message



broadgage

Posts: 1100
Joined: 07 August 2007

In practice it should be fine, 2.5mm cable on a 20 amp MCB, provided that the conditions do not require that the cable be de-rated to less than 20 amps.

Not strictly complliant with the regs though, since the design current is greater than the OCPD.

If both water heaters are used at the same time then the MCB should trip before any harm is done.
No worse than someone plugging in 10KW worth of portable heaters on a 20 amp radial circuit.
 26 June 2012 12:46 PM
User is offline View Users Profile Print this message



GB

Posts: 319
Joined: 04 September 2002

Not for Me!!

Understand the thinking but not sure it justifies the possible downsides, sometimes the client just has to cough up so we can sleep tight. fuses should be for emergency operation not to cover flaws in the design, if you put two taps on the fuse will "pop" aint a good way forward.

 26 June 2012 01:19 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9894
Joined: 13 August 2003

Isn't it permissible to design for thermally equivalent current rather than instantaneous current (a bit like diversity). I'm sure there is (or was) something in one of the GNs about it (sorry, I don't have it to hand at the moment).
- Andy.
 26 June 2012 01:30 PM
User is offline View Users Profile Print this message



GB

Posts: 319
Joined: 04 September 2002

Think I read something some where about that but thought it was to do with grouping factors?
May see if I can find the piece in a bit.