I have a 4 core 2.5 cable, 3phase earth running out to an isolator.
The SWA has a CSA of 20mm but is only the equivalent of a 6.43mm The regs say thew minimum CSA of a main protective bonding condutor should be no less than 10mm square. Can I use the SWA as my main protective conductor. I also have 3 seperate SWA cable running to the same isolator can I combine all 4 SWA and use it as my main protective bonding conductor. or do I need to run out a seperate earth cable. |
|
|
|
|
|
|
|
|
Hi, could you explain a bit clearer what you are trying to achieve, ie: where you already have a 2.5mm core and presumably the armour of the swa currently connected as the c.p.c, what is the reason that you need sufficient csa to use these connections as a main protective bonding conductor - will you be connecting from this isolator to extraneous conductive parts?
|
|
|
|
|
|
|
|
|
Maca
Your equivalent 6.43mm2 is only applicable if used as a cpc not bonding conductor. The copper equivalent is approximately 2.5mm2 Regards Jobbo |
|
|
|
|
|
|
|
|
i can't see how you can use multiple cables to make up a main bonding CSA. there is the obvious and likely possibility that some of them might get removed or altered at some point in the future.
Gary ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
|
|
|
|
|
|
|
|
Safety label in accordance 514.13.1 ?
Maybe not - OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
If the load is a motor on a VFD, then run a separate bonding conductor, as the SWA would be a screen, for the VFD noise in the cable, and the bonding conductor becomes the functional earth.
Best document for cabling a VFD is an ABB drive manual. Regards Derrick |
|
|
|
|
|