IET logo
 
IET
Decrease font size
Increase font size
Topic Title: Led flashing???
Topic Summary:
Created On: 20 June 2012 06:28 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 20 June 2012 06:28 PM
User is offline View Users Profile Print this message



Ben10

Posts: 26
Joined: 31 May 2012

Hello all
Just installed 9 LED lamps ( good quality) in a kitchen on a dimmer. When (dimmable) lamps are dimmed and the kettle is switched on the lamps all dim of their own accord. The original lamps I had installed went out all together. This does not happen though when lights are at full capacity. Occasionaly the lamps go into overide and have a disco!
I've changed the lamps, dimmer module, mcb and kettle and it is still happening. Im guessing that the surge of the 3 kw kettle is interupting the power to the LEDs but does anyone know how I can stop this happening?

Any ideas welcome
 20 June 2012 06:35 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5272
Joined: 04 July 2007

Check the volt-drop when the kettle is switched on!

Dave.
 20 June 2012 07:22 PM
User is offline View Users Profile Print this message



Ben10

Posts: 26
Joined: 31 May 2012

Im sure it will drop but any idea of how I can rectify this ? Short of rewiring the lighting circuit in the house
 20 June 2012 07:32 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5272
Joined: 04 July 2007

Check for loose connections in consumer unit on the supply side, high resistance connections between tails and main switch etc. will cause excessive volt-drop. Might be worth checking tails size too, maybe only 10.00mm and/or long run?
 20 June 2012 11:19 PM
User is offline View Users Profile Print this message



alancapon

Posts: 5519
Joined: 27 December 2005

I am assuming that you are using the correct type of dimmer for the LED modules - they should specify whether you need a "leading edge" or "trailing edge" dimmer.

Regards,

Alan.
 21 June 2012 02:34 AM
User is offline View Users Profile Print this message



microy

Posts: 315
Joined: 25 October 2005

Ben. You need a filter. Contact the manufacturer of the light fittings.