Topic Title: Eddy Current "Aluminum Plate"
Created On: 20 June 2012 03:37 PM
CPC
Hi all, needing a wee bit of advice/help.
We have a power perfector installed within one of our buildings & the contactor has used three single core 185mm2 coil end lead cables to supply the PP. The single core cables feeding the PP are glanded individually through the aluminum top plate of the PP through separate brass glands which have rubber inserts.
The question is, will this create/induce eddy currents?? The contractor said it wont because the plate is aluminum.
Your comments would be appreciated.
 20 June 2012 03:41 PM
Avatar for OMS.
It needs to be ferrous to allow the induction of eddy currents.
Aluminium is non magnetic (and non ferrous) so you won't have an eddy current effect.
It's why we use aluminium gland plates on big switchgear that has single core supplies
Failure is always an option
 20 June 2012 03:46 PM
CPC
Thanks for the speedy reply OMS.
CPC
 20 June 2012 05:35 PM
Avatar for BigRed.
BigRed
Hm, true, but doesn't old leccy meters depend on eddy currents in an aluminium plate to go round? Think of spinning an ally plate and put a strond hard disk mag next to it...
Just a thought...
 20 June 2012 05:49 PM
Avatar for rocknroll.
rocknroll
Just a thought...
Just a thought, is it not the case that aluminium is paramagnetic and iron is ferromagnetic, its all to do with the atoms, see I did learn something. LOL
"Take nothing but a picture,
"Oh! The drama of it all."
 20 June 2012 05:56 PM
Going back to my television engineer days I remember that the Philips video recorders, (mid 70's, N1500 series) had an Eddy current brake which consisted of an aluminium disc running beween two halves of an electromagnet which was connected to the motor servo circuit. Never quite understood how it worked but it did!
 20 June 2012 06:05 PM
Avatar for MrOther.
MrOther
No it won't that's why AWA and is seldom used as opposed to SWA for singles going into ferrous materials.
 20 June 2012 06:06 PM
Avatar for OMS.
Will you stop it !! -
Two atoms are walking down the street. Says one atom to the other, "Hey! I think I lost an electron!" The other says, "Are you sure??" "Yes, I'm positive!"
In the OPs situation, where is the strong permanent field coming from - will the paramagnetic effect of aluminium happen ?
 20 June 2012 06:35 PM
rocknroll
All materials have magnetic fields because electrons are constantly moving about, in ferromagnetic materials they are aligned so one magnetic component is stonger than the other, in paramagnetic materials the magnetic components are aligned so they cancel each other out.
It all comes down a sprinkling of quantum mechanics, the ability of a material to conduct magnetic flux is called relative permeability.
 20 June 2012 06:40 PM
Avatar for OMS.
Seldom - I'd say never.
And BS 7671 prohibits it anyway
 20 June 2012 06:42 PM
Avatar for OMS.
LoL - so it is rocket science after all !! -
 20 June 2012 06:53 PM
rocknroll
paulskyrme
What about the possible electrolytic corrosion between the Al & the Brass though?...
Electrochemical series anyone?
RnR, please don't start on such topics they give me headaches these days
Quantum things, the nearest I get is old episodes of Quantum Leap these days!
 20 June 2012 07:03 PM
Avatar for OMS.
Well Al will be the less noble - but I'd like to think there won't be too much of an electrolyte present around a brass gland and an Al gland plate
 20 June 2012 07:13 PM
Avatar for MrOther.
MrOther
AWA is not allowed?
 20 June 2012 07:32 PM
paulskyrme
OMS,
Are you sure about that?
Rain water, tap water, both good electrolytes as you know!
 20 June 2012 08:01 PM
Avatar for OMS.
AWA is not allowed?
AWA is allowed - single core SWA isn't
 20 June 2012 09:58 PM
Avatar for MrOther.
MrOther
AWA is not allowed?
For the reason of eddy currents? AWA is allowed though isn't it?
 20 June 2012 10:14 PM
Avatar for Dave69.
Dave69
should of used aluminum glands
 21 June 2012 09:59 AM
Avatar for OMS.
OMS,
For sure - but would you expect rain water or tap water on the alu gland plate on the top face of a power perfector in a switch room. Even if you do get a touch of moisture, the internal heating of the PP would evaporate (quickly) any liquid. I also wouldn't expect too much of an environmental humidity problem in a switchroom
Aluminium glands as mentiond above would be another option, but we dont know the cable type used
IET » Wiring and the regulations » Eddy Current "Aluminum Plate"