Topic Title: CU loaded with Rcbo's
Topic Summary:
Created On: 31 May 2012 09:02 PM
Status: Post and Reply
Linear : Threading : Single : Branch
1 2 Next Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 31 May 2012 09:02 PM
User is offline View Users Profile Print this message



kirchoffs

Posts: 125
Joined: 08 February 2010

Any comments welcome.

Carried out an cu change today ,new unit was a15-way Wylex with standard 100 DP main switch . Spec asked for all circuits to be protected by RCBO's, 11 in total.

The problem i encountered was the total lack of space,it was so tight for wiring space it was unbelievable about 25mm from top of the RCBO's to the neutral and earth bus bars.

Surely the manufacturers must try them themselves first?.

The reason i'm moaning is I've another five to do.

The only idea i can think of is too get a larger con unit and fit blanks on every other way. to give a bit more room for wiring.

As far as i can see MK,Crabtree,Volex,Contactum etc are all roughly the same height,I don't think any manufacturer has increased the height of the con units since RCBO'S have become more widely specified.

Does anyone know of a more sparkie friendly con unit?.

Regards Dominic
 31 May 2012 09:05 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

Stackable units?

Pre wired CU in to a connection box - not ideal but the CU could be built before you get to site.

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 31 May 2012 10:37 PM
User is offline View Users Profile Print this message



SKElectrical

Posts: 701
Joined: 01 February 2009

Compact rcbos.
in effect you have two busbars (1 x N and 1 x L) .
they are the same size as mcbs. cost about £14 each. sold by ex NAPIT inspector near to me.
Otherwise keep on practising with the wylex C/Us. Awful design though.
 31 May 2012 10:43 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

Originally posted by: SKElectrical

Compact rcbos.


Eaton?

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 31 May 2012 10:49 PM
User is offline View Users Profile Print this message



SKElectrical

Posts: 701
Joined: 01 February 2009

Originally posted by: Martynduerden

(Compact rcbos)

Eaton?


Haha at those prices!!!!

No they are SBS. perfectly good and robust.

Edited: 31 May 2012 at 10:58 PM by SKElectrical
 31 May 2012 10:52 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9776
Joined: 13 August 2003

Compact rcbos.

Garo do an reasonably extensive range (both 1- and 2-module, both DP switching) - http://www.meteorelectrical.co...cbo-s-mcb-s-rcd-s.html - and they'll marry up nicely with DP bus-bars (so no silly fly leads). The problem is that most of the DP bus-bars at the moment have a pretty small CSA - often 6mm2, 10mm2 at best (presumably down to our continental friends having low current supplies and preference for going 3-phase for anything larger).
- Andy.
 31 May 2012 10:59 PM
User is offline View Users Profile Print this message



rovermaestro

Posts: 7
Joined: 05 February 2012

Had a recent all rcbo CU change at home and the electrician used a metal 12 way Contactum enclosure. He said he uses the metal enclosures because they have a bit more room inside. Looks good enough high up on the hall wall.
 31 May 2012 11:01 PM
User is offline View Users Profile Print this message



SKElectrical

Posts: 701
Joined: 01 February 2009

Originally posted by: AJJewsbury

The problem is that most of the DP bus-bars at the moment have a pretty small CSA - often 6mm2, 10mm2 at best (presumably down to our continental friends having low current supplies and preference for going 3-phase for anything larger).

- Andy.


The ones made by SBS are standard busbars bent by hand. Currently the larger busbars are not manufactured with the necessary bends in the teeth.
 31 May 2012 11:04 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

Originally posted by: AJJewsbury

Compact rcbos.


Garo do an reasonably extensive range (both 1- and 2-module, both DP switching) - http://www.meteorelectrical.co...cbo-s-mcb-s-rcd-s.html - and they'll marry up nicely with DP bus-bars (so no silly fly leads). The problem is that most of the DP bus-bars at the moment have a pretty small CSA - often 6mm2, 10mm2 at best (presumably down to our continental friends having low current supplies and preference for going 3-phase for anything larger).

- Andy.


Andy have you looked at the MG DP dis boards ? not very domestic friendly but very good from memory seem to recall they were used alot on 110v

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 31 May 2012 11:48 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9776
Joined: 13 August 2003

Andy have you looked at the MG DP dis boards

I did - from what I recall they were only available in a very restricted size (8-module i.e. 4-ways max?) and I suspect bl****y expensive (at least their RCBOs were).
- Andy.
 01 June 2012 12:09 AM
User is offline View Users Profile Print this message


Avatar for sparkiemike.
sparkiemike

Posts: 1435
Joined: 24 January 2008

The wylex metal consumer units have a bit more space.

I have mentioned this to wylex at a few trade shows, all I get is waffle about a new RCBO that is comming out with a smaller form factor. They have been talking about this for 3 years now!!!
 01 June 2012 06:40 AM
User is offline View Users Profile Print this message



kirchoffs

Posts: 125
Joined: 08 February 2010

Thanks for all the response lads.

SKElectrical SBS compact RCBO's ?.

Sorry have seach high and low last night and could not find any manufacture under SBS.

Any chance of a link please.

Regards Dominic
 01 June 2012 09:08 AM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9776
Joined: 13 August 2003

I don't know of SBS, but here's one compact type: http://www.toolstation.com/sho...e+C/d190/sd3096/p97794 (but only in C type as far as I can tell).

Lots of the big manufacturers do 2-module 'MCB height' RCBOs (mostly for the continental market).

Garo do some interesting ones - http://www.meteorelectrical.co...cbo-s-mcb-s-rcd-s.html - but the terminals mean it's either cable-in-cable-out or trying to source unusual bus bars.

- Andy.
 01 June 2012 09:15 AM
User is offline View Users Profile Print this message



rougediablo

Posts: 101
Joined: 09 November 2011

On the front page of the June edition of the Denmans Connector there are a range of extra height CU's with RCBO's if it helps.
 01 June 2012 09:33 PM
User is offline View Users Profile Print this message



londonlec

Posts: 61
Joined: 29 November 2010

Wylex make an extra height version of their consumer units.

They have 'EH' on the end of the product code. No idea where my work get them from thought.
 01 June 2012 11:43 PM
User is offline View Users Profile Print this message



aargeitakis

Posts: 138
Joined: 14 July 2005

When it is time to test a board full of rcbo's is a great fun. Normally takes double time than a normal dual rcd ccu. We have one contract and the spec is to fit wylex 14-way ccu with 11 rcbo's. Its a great fun,


Regards

Paul
 01 June 2012 11:44 PM
User is offline View Users Profile Print this message



Zs

Posts: 2314
Joined: 20 July 2006

Kirchoffs, the hager ones are not bad ( and I agree about the wylex).

The new BG board supposedly leaves plenty of room at the top, but I have a few issues with their brass terminals failing on their sockets so I've not tried one yet.

Stay away from CED.... We've all been taking them back round here as quite a few fail from new.

Martyn did an all RCBO board for me last year and he put the RCBOs onto the DIN rail and all the neutral tails into the bar first of all. I have to say it was impressive and looked fairly spread out. Might be worth a try if you have a few to do.

Zs
 02 June 2012 01:26 AM
User is offline View Users Profile Print this message



SKElectrical

Posts: 701
Joined: 01 February 2009

Originally posted by: kirchoffs

SBS compact RCBO's ?.



Any chance of a link please.


There is no website! He emails you a 'catalogue' of products and prices.
I dont know how to "Private Message" you... but if you email me i will pass on his contact details, tel number, and email etc. In fact i will just forward his last email on to you.
MY EMAIL: sipoole@ymail.com
 02 June 2012 06:35 AM
User is offline View Users Profile Print this message


Avatar for amooramin.
amooramin

Posts: 109
Joined: 16 December 2008

It's really early morning of saturday and I am going to work , still sleepy.Am I mistaken for thinking we shouldn't use metal consumer unit in domestic installations? Please enlight me if I am wrong.

About SBS RCBOs, I used them couple of times, fantastic, same size of MCBs. Very good and friendly customer service.

Regards
Ramin
 02 June 2012 08:26 AM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 904
Joined: 19 March 2010

Nothing wrong with metal consumer units in domestic, but remember that on a tt the tails should be rcd protected if they enter a metal box!

-------------------------
Regard
Richard (Dick)

www.rllewellyn.co.uk