Topic Title: RING FINAL CIRCUIT
Topic Summary: Should they be banned for new work
Created On: 09 November 2011 07:33 PM
Status: Post and Reply
Linear : Threading : Single : Branch
<< 1 2 3 4 5 Previous Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 18 November 2011 09:21 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17567
Joined: 23 March 2004

Rings should not be the first choice for domestic installations. There I have said it.


Why not - whilst I appreciate many of the points you make are possible, in practice many of them aren't credible - next time your out and about take notice that we are not surrounded by charred hulks and dead bodies.

RFC's have done a sterling job in millions of properties for many years - the evidence simply doesn't support the vague hypothetical risks - which incidentally are also true for any other circuit topography.

Take a look at circuit design in detail - even fully compliant with BS 7671 it is possible to "design in" failure conditions - particularly for thermal withstand, overload and aspects where users deploy practices that are unusual (think of overloads between 1.13 and 1.45 x In for example where the design is totally reliant on cable standards and can easily allow thermal damage to occur).


Regards

OMS

-------------------------
Failure is always an option
 18 November 2011 05:40 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

Originally posted by: gkenyon

Originally posted by: Legh

Well, that's my brief tour into linguistics - better stick to flower arranging

Tis now all Greek to me
- exit stage left


No please don't go !

This institution retains the former IEE Arms, with the open book stating in Latin "Disce Doce", or "Learn and Teach" (if I remember correctly)

Pass the knowledge on, don't hide !

You can see the arms on the Royal Charter: http://www.theiet.org/about/vi...aws2008v2.cfm?type=pdf

And in colour on this page: http://www.theiet.org/resource...esearch/guides-iet.cfm


ACT 2 - enter right, right?

So what is the consensus about rings?
IMO
trees and bushes can lead to a level of confusion when inspecting and testing domestic installations
stars from an obvious point fed off a radial makes sense, particularly for lighting.

lollipops, now, appears to make sense when utilizing redundant cooker radials or where it is easier to run a radial to a point where sockets were to be installed, but would still lead to ambiguity when labeling. What would you call the circuit? 'Lollipop socket ' or socket lollipop or radial sub-main feeding ring?

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 18 November 2011 05:48 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17567
Joined: 23 March 2004

What would you call the circuit?


How about a "small power circuit"

OMS

-------------------------
Failure is always an option
 18 November 2011 06:25 PM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3328
Joined: 18 January 2003

Legh said
trees and bushes can lead to a level of confusion when inspecting and testing domestic installations


Surely not worse than RFC - especially if you believe GN 3 - which I usually don't .

Regards

Geoff Blackwell
 18 November 2011 06:37 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

When I Install in domestic properties I always give this question a bit of thought, since the RFC was devised electrical consumption has changed and increased beyond all recognition, generally though I end up with Ground floor ring, First floor ring, Kitchen Ring and Kitchen utility radial, it seems to work out well in most instances.

The Upstairs and Down stairs of most houses nowadays seems to be full of Electronic devices & gadgets, as for the kitchen there seems to be an increasing number of counter top appliances which are close to or fully rated rated. The Utility radial can encompass most of what I call permanently connected appliances such as Fridge freezers, Washing machines, dish washers, tumble dryers, warm drawers etc etc.

The Ring does seem to still have a place the only alternative i consider is a 20/32A radial per room.

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 18 November 2011 07:39 PM
User is offline View Users Profile Print this message


Avatar for JonSteward.
JonSteward

Posts: 517
Joined: 04 December 2007

A ring mains make a job more interesting.
Radials are mundane. Ring main faults scatter the brain.
Great.
 18 November 2011 10:45 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

Originally posted by: GeoffBlackwell

Legh said

trees and bushes can lead to a level of confusion when inspecting and testing domestic installations


Surely not worse than RFC - especially if you believe GN 3 - which I usually don't .

Regards

Geoff Blackwell


I can't see any confusion in GN3's method of testing RFCs - only in an inspector's interpretation of the resultant values given by their instruments.

Don't you think?

Leg

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 19 November 2011 05:45 AM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3328
Joined: 18 January 2003

I am not going to get involved in yet another discussion on the tests that some seem to think are necessary for RFC - I have said plenty on that in the past .

BS 7671 : 2008 612.2.2 simples .

Regards

Geoff Blackwell
 19 November 2011 06:43 PM
User is offline View Users Profile Print this message


Avatar for gkenyon.
gkenyon

Posts: 4391
Joined: 06 May 2002

Another controversial question.

OK, so a bridged ring makes it all but impossible to test.

But surely it's generally safer than a broken ring, and when a single break, safer than a broken ring alone?

-------------------------
Eur Ing Graham Kenyon CEng MIET
 19 November 2011 07:55 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5292
Joined: 18 January 2003

I changed a consumer unit for one of my neighbours where the kitchen fitter installed a "lollipop" ring to the kitchen, a 6mm t+e to a hidden junction box from where a 2.5mm t+e ring was supplied, I took a socket off in the kitchen and tested the ring section and assessed the radial section as best I could only having access to one end of it.

I would quite happily condemn it, however I reported what I found and wrote it up on the report and left it at that as is the current thinking of dealing with such matters.

Nothing wrong with rings, but I have opted for radials recently for different reasons, where there is insulation it is easier to rate the 2.5mm t+e at 16 amps and have two 16 amp radial circuits than rate the cable at 20 amps and have one 32 amp ring circuit or start installing rings with oversized circuit conductors.


Andy
 19 November 2011 09:04 PM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 901
Joined: 19 March 2010

Originally posted by: sparkingchip

I changed a consumer unit for one of my neighbours where the kitchen fitter installed a "lollipop" ring to the kitchen, a 6mm t+e to a hidden junction box from where a 2.5mm t+e ring was supplied, I took a socket off in the kitchen and tested the ring section and assessed the radial section as best I could only having access to one end of it.

Andy


I expect if you look at the walls for imperfections, you'll see where the big old cooker control panel used to be. With a bit of digging you'll probably find a block of connectors plastered away in there, maybe even taped up!

-------------------------
Regard
Richard (Dick)

www.rllewellyn.co.uk
 19 November 2011 09:46 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5292
Joined: 18 January 2003

I happen to know this was a brand new circuit, the original cooker circuit was used to supply a SFCU to the cooker hood, gas hob ignition and single electric oven plugged into sockets on the lollipop circuit.

Seeing as we are only supposed to report dangers and potential dangers rather than maybe not complying with the regs then it isn't a big issue is it?

Andy
 19 November 2011 09:53 PM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 901
Joined: 19 March 2010

No issue at all for me if it meats circuit design criteria. As you say, we don't inspect cables under floors or burried in walls on a PIR, so perhaps the only non compliance is an inaccesible junction box

-------------------------
Regard
Richard (Dick)

www.rllewellyn.co.uk
 19 November 2011 10:00 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 6879
Joined: 23 April 2005

dick

'it meats circuit design criteria'

No beef with that then?

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 19 November 2011 10:07 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

Originally posted by: John Peckham

dick

'it meats circuit design criteria'

No beef with that then?


Now cow John

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 19 November 2011 10:08 PM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 901
Joined: 19 March 2010

That's what comes with having a vegetarian missus John. We had Chinese takeaway this evening, and I got to have some nice beef in black bean sauce, so the meat must have gone to my head!

-------------------------
Regard
Richard (Dick)

www.rllewellyn.co.uk
 20 November 2011 06:47 AM
User is offline View Users Profile Print this message


Avatar for ebee.
ebee

Posts: 5365
Joined: 02 December 2004

When does your local vegetarian club have the next meating?

-------------------------
Regards,
Ebee (M I S P N)

Knotted cables cause Lumpy Lektrik
 20 June 2012 10:22 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5292
Joined: 18 January 2003

NICEIC have a article in the Professional Electrician magazine saying "Lollipop" circuits are OK.

Andy
 20 June 2012 10:26 PM
User is offline View Users Profile Print this message


Avatar for gkenyon.
gkenyon

Posts: 4391
Joined: 06 May 2002

Originally posted by: sparkingchip

NICEIC have a article in the Professional Electrician magazine saying "Lollipop" circuits are OK.



Andy
Why shouldn't they be, all else being equal, provided you can get at the JB (or other type of "accessory" or "equipment") to carry out the RFC continuity test?

-------------------------
Eur Ing Graham Kenyon CEng MIET
 21 June 2012 07:05 AM
User is offline View Users Profile Print this message


Avatar for ebee.
ebee

Posts: 5365
Joined: 02 December 2004

I`d love to see comments on what I called a "Butterfly" (I`d call it figure of eight but a fig of 8 already exists) - two rings with one fuseway, being one circuit by definition or even three/four rings ("clover" perhaps) all obeying circuit lengths/floor space served and loading considerations etc
as one would with a proper ring.

Not nice to test perhaps but being non conventional does it make it unsafe/poor practice?

-------------------------
Regards,
Ebee (M I S P N)

Knotted cables cause Lumpy Lektrik