 09 November 2011 10:12 PM
User is offline View Users Profile Print this message



Paul1966

Posts: 1538
Joined: 21 December 2004

Rings were something of a kludge when they were introduced, and nothing much has changed since. I'd be quite happy to see them abandoned.
 09 November 2011 10:25 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

Dave,
Don't I know it, the theory is one thing but finding the problem socket, broken conductor is something to be experienced.
The one thing that cheeses me off, you can spend a day chasing a fault around and the customer then says. 'what exactly have you done today to earn all this money ?'.
I then have to explain the first class airfare to the Seychelles is rather expensive you know!

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 09 November 2011 10:28 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 6880
Joined: 23 April 2005

So adding to the proposed death of rings we have spur upon spur from rings, over lapping rings, radials run from rings, single rings run from 2 different circuit breakers or fuses, the difficulty of tracing faults etc. etc.

The potential to screw things up by the new breed of semi skilled installlers and DIYers it is not looking good for these UK strange circuits.

Putting the advantages of RFCs against the disadvantages in the pans of the scales it could be curtains for RFCs?

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 09 November 2011 10:37 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9795
Joined: 13 August 2003

To me as a person who has to test RFCs they are a pain in the backside.

Oddly, the testing of radials is a lot less thorough than of rings. Rings get N continuity checked, standard tests on radials don't. L-PE reversals on rings would be spotted, no so on a radial if the standard R1+R2 test is used. But surely that's a feature of the tests rather than the ring itself.

If you has to test radials just as thoroughly as rings (say with an additional R1+Rn test at all points), together with perhaps a greater number of circuits to test, would the difference be that great?

- Andy.
 09 November 2011 10:46 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

So adding to the proposed death of rings we have spur upon spur from rings, over lapping rings, radials run from rings, single rings run from 2 different circuit breakers or fuses, the difficulty of tracing faults etc. etc


Most of these faults are not actually dangerous when you think of the protective devices that are now installed.

None of them comply with the regs , of course

Where MCBs and RCDs are used then the danger from most of these faults reduces considerably.... as it were.

I remember a conversation I had with some chap about the use of RCDs and how they would cover a multitude of sins.!

Spur upon spur - I have never seen a real dangerous problem

overlapping rings - only if you load them irregularly with heating appliances.

radials run from rings - possibly volt drop but overload is unlikely with present type of loading and no chance under short circuit conditions using MCBs

A ring split across two MCBs - that's a definite no no and is dangerous to the uninitiated that must be corrected !

Radials are much easier to negotiate

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 09 November 2011 10:59 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17594
Joined: 23 March 2004

A ring split across two MCBs - that's a definite no no and is dangerous to the uninitiated that must be corrected !


Although we see no drama in that scenario with "ring mains" - I've seen plenty of them with 2 x 300mm conductors into 630A ACB's on either end of a dual fed switchboard.

Most of these faults are not actually dangerous when you think of the protective devices that are now installed.


Exactly - only dangerous in the minds of the inspector, who equates lack of compliance with BS 7671 as dangerous without thinking through the actual risk

Regards

OMS

-------------------------
Failure is always an option
 09 November 2011 11:04 PM
User is offline View Users Profile Print this message



Zs

Posts: 2316
Joined: 20 July 2006

I love this thread.

When you work on your own for much of the time, or are the only electrician on site, you gently develop your own views.

No, do not ban ring finals. Keep the choice.

Every time Dave Parry posts an opinion on one of these discussions I wonder if we are living in a parallel universe. I agree with Dave all the way. Further, we know when a simple radial is the quickest and easiest to install. Or even the most appropriate. It is ok for the UK electrical engineer to be the finest. For Him to be trusted to make a call on how to install without dictate. Even the regs are now quietly indicating UK regs against harmonised ones, if you know what to look for.

Testing a RF is peasy. Testing a radial means finding the end of it.

Fault finding a RF may be a little more complex, but fault find it we do.

Spell-checking a post on the other hand. . . Now that's a toughy

Zs
 09 November 2011 11:58 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

Originally posted by: OMS

A ring split across two MCBs - that's a definite no no and is dangerous to the uninitiated that must be corrected !


Although we see no drama in that scenario with "ring mains" - I've seen plenty of them with 2 x 300mm conductors into 630A ACB's on either end of a dual fed switchboard.

I've done work in a few LV mains switch room cabinets but never worked on a duel fed compressed air switches before so this another starting point of my educational process......

Most of these faults are not actually dangerous when you think of the protective devices that are now installed.


Exactly - only dangerous in the minds of the inspector, who equates lack of compliance with BS 7671 as dangerous without thinking through the actual risk

agreed, but we all have our relative starting points .... It's difficult to get a start when you've been on your own for so long

Regards

OMS


Legh

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 10 November 2011 12:15 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17594
Joined: 23 March 2004

Originally posted by: Legh

Originally posted by: OMS

A ring split across two MCBs - that's a definite no no and is dangerous to the uninitiated that must be corrected !


Although we see no drama in that scenario with "ring mains" - I've seen plenty of them with 2 x 300mm conductors into 630A ACB's on either end of a dual fed switchboard.

I've done work in a few LV mains switch room cabinets but never worked on a duel fed compressed air switches before so this another starting point of my educational process......

ACB's - air circuit breakers - they use air (rather than liquid) as the arc quenching medium (via splitters and arc chutes) - they are usually motor rather than air driven. These are not necessarily the same as gas quenched (say SF6) or vacuum operated breakers (the latter two usually being HV rather than LV types).

It's quite common for resilient LV supplies to arrange primry and secondary distribution as ring mains fed from two breakers (although they may not always be operated as ring closed due to elevated fault levels)

Most of these faults are not actually dangerous when you think of the protective devices that are now installed.


Exactly - only dangerous in the minds of the inspector, who equates lack of compliance with BS 7671 as dangerous without thinking through the actual risk

agreed, but we all have our relative starting points .... It's difficult to get a start when you've been on your own for so long


Perhaps - but thinking through the problem is as important as blindly repeating available guidance in every circumstance don't you think

Regards

OMS


Legh


OMS

-------------------------
Failure is always an option
 10 November 2011 12:42 AM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

Perhaps - but thinking through the problem is as important as blindly repeating available guidance in every circumstance don't you think


I've been at it for a few years so its not all blindly regurgitating the fuel that is fed into the machine ... and as for the duel fed ACB switching devices I'll get back to you ...eventually .. as they say, 'seeing is believing'!

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 10 November 2011 12:55 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17594
Joined: 23 March 2004

Try a google for HTM 06-01 - that should have examples of duel unified supplies within a healthcare environment. Trust me they do exist

Try here

Page 39 - Substation ISS switchboard shows a duel fed ring from each half of the duel fed switchboard feeding risk category 4 and 5 services (in this instance into a UPS but that could also be a switchboard)

Regards

OMS

-------------------------
Failure is always an option
 10 November 2011 01:19 AM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3153
Joined: 17 December 2004

OMS,
Thanks for the information, some of those diagrams look familiar.
I've had enough for tonight
good night!

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 10 November 2011 01:26 AM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

Having a RFC on two fuses was quite common when they were first introduced.
A number of 15A radials were converted to RFCs by simply connecting the ends of the radials together.
Then again fuses in neutrals were allowed by the then Regulations.
No I wouldn't advocate the banning of RFCs, to my mind they are versatile, cheaper and easier to install or adapt than the alternative.
 10 November 2011 07:55 AM
User is offline View Users Profile Print this message



Angram

Posts: 537
Joined: 23 March 2009

It must be frustrating for suppliers of protective devices outside the UK to see the lost sales that Ring Circuits mean to them.

Why don't they put maximum pressure on the UK in committees to make us "harmonise" like "good" Europeans ?
 10 November 2011 10:16 AM
User is offline View Users Profile Print this message



broadgage

Posts: 1082
Joined: 07 August 2007

I can see both sides of the argument for and against ring finals, but can also see an argument for retaining them, that no one else has mentioned.

Changes to the regulations are not normally intended to be retrospective, yet many seen to regard thaem as being retrospective.

IF ring finals WERE banned for new installs, then it would not be long until "inspectors" start giving code ones to every existing ring final.

Remember the relatively new requirement that most socket outlets in most situations should be RCD protected ?
There are many reports of installations only a few years old, and correct at the time, being given "code 1" or bet best "code 2" for non RCD sockets.

There is a very general view among non electricians, that continuall changes to regulations are a money making scam.
If installations done only a few years ago by reputable contractors now need renewing before a house can be sold, no wonder people are cynical.
 10 November 2011 10:54 AM
User is offline View Users Profile Print this message


Avatar for Jobbo.
Jobbo

Posts: 893
Joined: 08 July 2010

I thought that the IET and the ECA documented a study on ring final circuits and radials a few years ago. The conclusion being RFC were safer due to there being 2 x cpc at each socket. Anyone still got a copy of this? I'll have a dig for it when I'm back in the office

As for testing them, I agree they are a pain. Nothing like a dozen RFC to take the smile off your face

Regards

Jobbo
 10 November 2011 11:54 AM
User is offline View Users Profile Print this message



Jaymack

Posts: 4291
Joined: 07 April 2004

A ring circuit per se, is quite common in industry, to give a greater measure of security for L.V., M.V. and H.V. circuits, e.g. airport perimeter lighting etc.,etc. I imagine that the principle was adopted for the domestic ones from these, in the industrial case though, they are usually for security of supply; and in most cases here, they have time graded directional protection.

The main reason usually given for the introduction to the domestic and commercial scene, was they were more economical to install than radial circuits. All in all, I see nought wrong with them if they are correctly installed and maintained, e.g. using the correct fuse sizes. I suspect that the yanks would be using more of the principle, if they had thought of them first.

Lets face it, they're the only real challenge for wiring on the "home" front.

Regards
 10 November 2011 02:26 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3181
Joined: 13 July 2008

Originally posted by: OMS

In my opinion john - RFC's are a perfectly good circuit design for flexibility, convenience, safety and security of supply.


Is that not like saying "my connections might be dodgy so I will connect at both ends to double my chances"


If we want to go continental then fine - but lets bin the 13A socket outlet whilst we are about it.


Now now we will be in the Euro if you continue down that route!


...... and educate installers better


Daydream believer!

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 10 November 2011 03:16 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17594
Joined: 23 March 2004

Originally posted by: Martynduerden

Originally posted by: OMS

In my opinion john - RFC's are a perfectly good circuit design for flexibility, convenience, safety and security of supply.


Is that not like saying "my connections might be dodgy so I will connect at both ends to double my chances"

Not really Martyn - although we do that for protective conductor currents.

It's flexible in terms of where the loads may be connected, it's convenient in terms of a large number of outlets over a given area, it's a pretty safe design and it's secure if you need to operate with partial damage. Doubling the chances is down to poor installation.


If we want to go continental then fine - but lets bin the 13A socket outlet whilst we are about it.


Now now we will be in the Euro if you continue down that route!

Maybe, but Europe is a big trading area - we are better off on the inside ***** out for sure

...... and educate installers better




Daydream believer!

Maybe - but it's not that hard to get 6 ccores into a semblance of order is it


Regards

OMS

-------------------------
Failure is always an option
 10 November 2011 07:09 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5272
Joined: 04 July 2007

Every time Dave Parry posts an opinion on one of these discussions I wonder if we are living in a parallel universe
--------------------------------------
Many thanks for that comment ZS, it's nice to know who of us are on the same wavelength!

regards,

Dave.