Topic Title: U,V,W, R,S,T vs L1,L2,L3
Created On: 30 September 2011 10:40 AM
timothyboler
I've just been looking at a generator set and the busbars in the terminal box are labeled U,V,W, in accordance with IEC 60034-8 "Terminal markings and direction of rotation" (had to look that up because at first I thought that was incorrect and should have been L1, L2, L3 :-/). However the corresponding switchgear is marked R,S,T instead of L1, L2, L3. I've not seen that before and wondered if anyone knew the standard that it came from?
 30 September 2011 10:51 AM
rocknroll
In a three-phase generator there are three windings, typically designated as A-B-C, R-S-T or U-V-W.
Phase rotation (or phase sequence) describes the order (A-B-C, R-S-T, or U-V-W) of the phase voltages at the output terminals of a three-phase generator. The generator phase rotation must match the facility phase rotation.
So if the facility phase rotation is R-S-T then U to R, V to S and W to T.
"Take nothing but a picture,
"Oh! The drama of it all."
 30 September 2011 05:07 PM
Paul1966
These designations come from the old Continental standard which goes right back to the early days of three-phase equipment.
R-S-T was the general designation for the three phases of the supply system.
U-V-W and X-Y-Z were then used to designate the connections to the windings on motors, generators, etc. The individual windings were U to X, V to Y, and W to Z. So for a wye generator configuration, for example, X, Y, and Z would be strapped together to form the neutral point, and the phases R, S, and T would be fed from the U, V, and W winding terminals respectively.