Test readings on ground source heat pump are showing R1 + R2 as 0.03 ohms, zs reading taken at rotary isolator for the pump is 0.27 ohms. Protective device is a 63A type d mcb, run of cable is approx 7 metres, wired in 16mm t & e, ze is 0.11 ohms, max for a type d is 0.15 ohms so i'm well over but how come given all the other readings. Advice needed please
|
|
|
|
|
|
|
|
|
What tester have you used, and on what setting? Is there an associated RCD on the circuit?
------------------------- Regard Richard (Dick) www.rllewellyn.co.uk |
|
|
|
|
|
|
|
|
calculate your zs from your r1 + r2 reading.
the quality of your lead connection and the accuracy of your meter can affect the readings quite a lot, especially if its through an rcd. ( the last one i did had to have a 100m/a rcd on it ) . Gary ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
|
|
|
|
|