Topic Summary:
Created On: 27 August 2011 07:34 AM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 27 August 2011 07:34 AM
User is offline View Users Profile Print this message



jonah71

Posts: 41
Joined: 05 March 2006

Test readings on ground source heat pump are showing R1 + R2 as 0.03 ohms, zs reading taken at rotary isolator for the pump is 0.27 ohms. Protective device is a 63A type d mcb, run of cable is approx 7 metres, wired in 16mm t & e, ze is 0.11 ohms, max for a type d is 0.15 ohms so i'm well over but how come given all the other readings. Advice needed please
 27 August 2011 08:00 AM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 1150
Joined: 19 March 2010

What tester have you used, and on what setting? Is there an associated RCD on the circuit?

-------------------------
Regards
Richard (Dick)

"Insert words of wisdom and/or witty pun here"
 27 August 2011 09:08 AM
User is offline View Users Profile Print this message



aligarjon

Posts: 2866
Joined: 09 September 2005

calculate your zs from your r1 + r2 reading.
the quality of your lead connection and the accuracy of your meter can affect the readings quite a lot, especially if its through an rcd. ( the last one i did had to have a 100m/a rcd on it ) .

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese