Topic Title: Crimping solid core cables
Topic Summary: yes or no?
Created On: 13 July 2011 08:30 PM
Status: Post and Reply
Linear : Threading : Single : Branch
<< 1 2 3 Previous Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 03 July 2012 11:09 PM
User is offline View Users Profile Print this message



sizzler

Posts: 21
Joined: 02 November 2007

Note 2 on section 526.2 of BS7671 (aka 17th edition the wiring regs), which states: "Terminals without the marking R (only rigid conductor), F (only flexible conductor), S or Sol (only solid conductor) are suitable for the connection of all types of conductors
 04 July 2012 01:23 AM
User is offline View Users Profile Print this message



djrichiet

Posts: 82
Joined: 23 April 2010

Never crimp solid conductors - it takes a small amount of expansion/contraction for them to come loose. Seen it happen a few times myself. If you HAVE to use a crimp lug on a solid conductor then instead of crimping, use solder as it provides an excellent termination. Often I have stripped the outer coloured sleeve, soldered then used a decent brand heat shrink (such as Tyco) after.

-------------------------
From SMD's to 132kV... ive had a go!

Richard Talmage, LCGI EngTech TMIET
 04 July 2012 08:17 AM
User is offline View Users Profile Print this message



Jaymack

Posts: 4290
Joined: 07 April 2004

Originally posted by: djrichiet
Never crimp solid conductors - it takes a small amount of expansion/contraction for them to come loose. Seen it happen a few times myself.

Because of inadequate crimping or temperature cycling?

If you HAVE to use a crimp lug on a solid conductor then instead of crimping, use solder as it provides an excellent termination.

I wouldn't recommend soldering, it's time consuming and also needs skill, not to mention the behaviour under fault conditions. Also, soldering of small, flexible core sizes is not allowed to BS 7671.

I wouldn't butt the ends of cores for ferrules, rather have the cores overlapping, use 2 points of crimping with the correct tool size, and carry out the tug test.

Regards

Edited: 04 July 2012 at 08:26 AM by Jaymack
 04 July 2012 09:32 AM
User is offline View Users Profile Print this message


Avatar for BigRed.
BigRed

Posts: 506
Joined: 10 November 2006

Regarding 2.5mm crimping, it can be done with uninsulated crimps and a raychem adhesive heat shrink cap end.fiddly as hell though!
Did seriously rethink after this thread started though