Topic Title: ZS Testing/explained
Topic Summary: Ceiling Rose
Created On: 09 February 2011 09:04 PM
Status: Post and Reply
Linear : Threading : Single : Branch
1 2 Next Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 09 February 2011 09:04 PM
User is offline View Users Profile Print this message



nige296

Posts: 74
Joined: 04 December 2009

Testing ZS at a ceiling rose, not practical to undo the rose to get an earth connection, however I can toggle my fluke to L-N and get a ZS reading. Is this acceptable and if so my understanding of a ZS test is an earth fault loop impedance test! So if testing without the earth how can it be a ZS test, anybody explain why, Many thanks
 09 February 2011 09:08 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 6200
Joined: 04 July 2007

You can't do a Zs test without connecting to the earth can you! Zs is the earth loop between L & E.
 09 February 2011 09:13 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4439
Joined: 10 December 2004

I'm assuming that this is a PIR, and if so then LIM would be perfectly acceptable in the circumstances you describe.
However not being conversant with your tester myself, I suggest you look at the technical specifications or hand book.
It may be that this particular test only works on TN-C-S systems, or it may be a guesstimate, and you are required to select cable type, or input the CSA of the CPC.
 09 February 2011 09:31 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 6031
Joined: 18 January 2003

NO NO NO!

You are trying to prove an earth connection exists, so only testing the earth will do.

However you can test on a sampling basis so don't need to disassemble every fitting unless problems are showing up elsewhere.

Also if the switch earth is connected to the one at the light and the switch is OK then logically the light should be OK as well.

Andy
 09 February 2011 09:33 PM
User is offline View Users Profile Print this message



primo

Posts: 434
Joined: 10 January 2008

If you use the L-N setting this will give you a high current test between whichever conductors you put it on. If it is going on line and neutral then it will give you the line-neutral impedance, if you put it on line-earth it will give you the EFLI (but may trip the breaker and RCD if present).

So in your case you are not testing Zs for the circuit.
 09 February 2011 09:34 PM
User is offline View Users Profile Print this message



PatHammond

Posts: 215
Joined: 04 December 2008

When you toggle it on the Fluke you are measuring the L-N loop not the L-E loop therefore you are not measuring the Zs or the Ze. The purpose of the toggle is to allow you to measure the prospective fault current which will be the higher reading of either the PEFC ie the Ze/Zs at that point in the installation or the PSCC ie L-N loop (short circuit)

-------------------------
4.5 day wonder...had to start somewhere
 09 February 2011 09:38 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 6200
Joined: 04 July 2007

You would use the L-N range on your Fluke if you were doing a L-N loop test or measuring PFC for instance, you can also use the L-N range for carrying out a 2 lead Zs test but in this case you would still need to test between L-E or it wouldn't be a Zs test! (it will also trip the rcd if one is in circuit) If it is a pir, surely there is some other point that's more accessible?
 09 February 2011 09:39 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4439
Joined: 10 December 2004

A Zs test is not to prove an earth connection exists, although it would do so, but to prove that the CPD would operate within the time required by BS7671.
Smpling should be of circuits, not equipment of a circuit that is being tested.
 09 February 2011 09:41 PM
User is offline View Users Profile Print this message



ant1uk

Posts: 2376
Joined: 22 June 2010

Line Impedance
Line impedance is source impedance measured between Line conductors or
Line and Neutral. This function allows the following tests:
. Line to Neutral loop impedance.
. Line to Line impedance in 3-phase systems.
165XB
Users Manual
22
. L-PE loop measurement. This is a way of making a high current, 2-wire
loop measurement. It cannot be used on circuits protected by RCDs
because it will cause them to trip.
. Prospective Short Circuit Current (PSC). PSC is the current that can
potentially flow if the phase conductor is shorted to the neutral conductor or
another phase conductor. The tester calculates the PSC current by dividing
the measured mains voltage by the line impedance.

To measure line impedance:
1. Turn the rotary switch to the x position. The LCD indicates that the
high current loop mode is selected by displaying the o symbol.
2. Connect the red lead to the L (red) and the blue lead to the N (blue)
terminals of the tester.
3. Press 1 to select L-N.
4. Use the zero adapter to zero the test leads or the mains cord.
5. Press and hold Z for more than two seconds until the ZERO
annunciator appears.
 09 February 2011 09:41 PM
User is offline View Users Profile Print this message



PatHammond

Posts: 215
Joined: 04 December 2008

Originally posted by: daveparry1

You would use the L-N range on your Fluke if you were doing a L-N loop test or measuring PFC for instance, you can also use the L-N range for carrying out a 2 lead Zs test

Hi Dave what is a 2 lead Zs test; I thought most testers needed a neutral for 'balancing' purposes...whatever that means

-------------------------
4.5 day wonder...had to start somewhere
 09 February 2011 09:48 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 6200
Joined: 04 July 2007

Hi Pat, you can do a 2 lead Zs or Ze test with the Fluke, but it will trip rcd's in the case of Zs tests as it's a high current test.
 09 February 2011 09:55 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 6031
Joined: 18 January 2003

GN3 (2002 edition) page 71 paragraph 3.9.1 a joints and connections page 71 also note 2 to table 3.3 page 78 oh! also note 4 of the same table.

Andy
 09 February 2011 11:28 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 7457
Joined: 23 April 2005

Nige296

Given your question do you think you are competent to carry out this testing?

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 10 February 2011 01:41 PM
User is offline View Users Profile Print this message



seeker

Posts: 319
Joined: 10 March 2007

Originally posted by: John Peckham

Nige296



Given your question do you think you are competent to carry out this testing?


Not one of your students I take it John?
 10 February 2011 02:26 PM
User is offline View Users Profile Print this message



ant1uk

Posts: 2376
Joined: 22 June 2010

Originally posted by: nige296

Testing ZS at a ceiling rose, not practical to undo the rose to get an earth connection, however I can toggle my fluke to L-N and get a ZS reading. Is this acceptable and if so my understanding of a ZS test is an earth fault loop impedance test! So if testing without the earth how can it be a ZS test, anybody explain why, Many thanks


This is not an Earth Loop Impedance then is it, This will be a line to neutral impedance you will be measuring. The fluke certainly does have this option but also is used to measure PSC at the same time.
 10 February 2011 11:02 PM
User is offline View Users Profile Print this message



gpaul2

Posts: 416
Joined: 16 February 2006

Originally posted by: daveparry1

You can't do a Zs test without connecting to the earth can you! Zs is the earth loop between L & E.


that is something what my old boss would say along with a smack around the ears
 11 February 2011 12:13 AM
User is offline View Users Profile Print this message


Avatar for Dale76uk.
Dale76uk

Posts: 412
Joined: 04 February 2010

Why are you carrying out a Zs at a ceiling rose?? EAWR 1989 reg 14

Just calculate it!
 11 February 2011 12:20 AM
User is offline View Users Profile Print this message



John Peckham

Posts: 7457
Joined: 23 April 2005

Dale

You have done it now. I raised te issue of calculating Zs on the forum sometime ago after watching the NICEIC Domestic PIR DVD. On the DVD Tony Cable derives the value of Zs from Ze + R1 +R2 pointing out compliance with Regulation 14. Having looked at I agree you should not live test Zs if you can avoid to comply with Reg.14.

Well the old school on the forum thought this was an assault on their experience, knowledge and man hood. The tuskers came roaring out of the long grass and I had to retreat.

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 11 February 2011 12:21 AM
User is offline View Users Profile Print this message



ant1uk

Posts: 2376
Joined: 22 June 2010

Originally posted by: Dale76uk

Why are you carrying out a Zs at a ceiling rose?? EAWR 1989 reg 14

Just calculate it!


And why would this be? Is it dangerous?
 11 February 2011 07:27 AM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 1150
Joined: 19 March 2010

Am I being thick if I ask what is not practical about undoing a ceiling rose?

-------------------------
Regards
Richard (Dick)

"Insert words of wisdom and/or witty pun here"