A little help in filling out one of these electrical installation forms.
On the schedule of inspections report do the boxes conform to the exisiting installation or to the work you have done?
I.e if i were to just fit a consumer unit obviously some of the boxes wouldnt need ticking ie Selv box etc..
My question is do i tick thes as na or as present?
Any help would be appreciated
 07 February 2011 11:29 PM
Becklec
They are asking you what you have checked.....
.....If you have checked it and it is ok, put a tick....
.....If you have checked it and it is not ok, enter a cross....
.....If it is not there to check, enter N/A.....
....Never leave a box blank, it looks like you have missed the question.
hope that helps.
Btw, a DB change would normally call for a complete periodic as you are reconnecting existing unknown circuits into a piece of kit that you are now responsible for.
As well as a installation cert for the DB itself.
remember it is better to be safe than sorry.
Becklec.
 07 February 2011 11:33 PM
Tick the boxes that apply to the note's you put in the "extent of installation covered by this certificate" box.
ukghost
Thanks for the help
 07 February 2011 11:36 PM
No it wouldn't athough it would require a full test of all circuit's and an EIC.
 08 February 2011 12:43 AM
spinlondon
The schedules of inspections and tests relate to the work you have conducted.
If you want to include more, there is nothing preventing you from doing so.