Topic Title: zoning of fire alarm in commercial--residential combined building
Topic Summary:
Created On: 13 December 2010 12:31 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 13 December 2010 12:52 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19463
Joined: 23 March 2004

What does the fire risk assessment say ?

I suspect you'll have independent systems for the shop and common parts to BS 5839 Part 1, and Part 6 systems in the flats. It will depend on other factors in the FRA if you take sounders from the Part 1 system into the flats.

Key issue is to recognise if the flats have a defend in place strategy

Regards

OMS

-------------------------
Failure is always an option
 13 December 2010 01:46 PM
User is offline View Users Profile Print this message



eamonn1983

Posts: 88
Joined: 21 October 2010

The apartments will have a heat wired in kitchen and sounder in hall of the system and a mains oPerated smoke alarm in hall