Morning all
I have been asked to install 4 of 400w metal halide light assys in an outside yard. without manufacturers data would the following calculation be reasonable and acceptable to calculate the design load using 0.8 as a pf. i remember back from college that this was the factor to use then but is it still ok as a rule of thumb at present.

400w x 4 = 1600w 1600w / 230 x0.8= Ib

Could this same calculation also be used for high pressure sodium and fluorescent lighting assy,s

many thanks

Regards Martin
 07 November 2010 12:05 PM
User is offline View Users Profile Print this message


Avatar for rocknroll.
rocknroll

Posts: 8808
Joined: 03 October 2005

In the absence of manufacturers data the factor for discharge lighting is 1.8

4 x 400 x 1.8 / 230 = Ib

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------
 07 November 2010 12:19 PM
User is offline View Users Profile Print this message


Avatar for dg66.
dg66

Posts: 1649
Joined: 11 January 2008

The 1.8 factor that RnR has mentioned is to account for control gear losses which result in additional current,and the possible introduction of harmonics from the control gear.

-------------------------
Regards

Dave(not Cockburn)
 07 November 2010 02:32 PM
User is offline View Users Profile Print this message



12216

Posts: 45
Joined: 22 August 2010

Many thanks to you both.

just out of curiosity when do you use the following P / V x 0.8 ( based on 230v supply)
 07 November 2010 02:50 PM
User is offline View Users Profile Print this message


Avatar for rocknroll.
rocknroll

Posts: 8808
Joined: 03 October 2005

You cant just use it on its own, you have to use it in conjuction with data about power losses, harmonic currents and p.f.

Lets take some live data from a manufacturer;

400W lamp
20% control gear losses (in real terms this is more like 25% or 100W)
Harmonic current of 0.598A
Power factor of 0.9

If we do the calc using the recommended 1.8 factor all we need to do is,

400 x 1.8 / 230 = an Ib of 3A.

Now using the manufacturers data above,

400 + 100 (losses) / 230 x 0.9 (p.f.) = 2.4A

2.4A + 0.589A (harmonic current) = an Ib of 2.98A

How close is that then

Note that the 1.8 factor is only good for a power factor down to 0.65/0.7 after that then you need to use manufacturers data.

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------

Edited: 07 November 2010 at 03:32 PM by rocknroll
 07 November 2010 05:44 PM
User is offline View Users Profile Print this message



12216

Posts: 45
Joined: 22 August 2010

Originally posted by: rocknroll

You cant just use it on its own, you have to use it in conjuction with data about power losses, harmonic currents and p.f.



Lets take some live data from a manufacturer;



400W lamp

20% control gear losses (in real terms this is more like 25% or 100W)

Harmonic current of 0.598A

Power factor of 0.9



If we do the calc using the recommended 1.8 factor all we need to do is,



400 x 1.8 / 230 = an Ib of 3A.



Now using the manufacturers data above,



400 + 100 (losses) / 230 x 0.9 (p.f.) = 2.4A



2.4A + 0.589A (harmonic current) = an Ib of 2.98A



How close is that then



Note that the 1.8 factor is only good for a power factor down to 0.65/0.7 after that then you need to use manufacturers data.



regards


Many thanks RnR for your time on this one.

Regards

Martin
 07 November 2010 05:44 PM
User is offline View Users Profile Print this message



12216

Posts: 45
Joined: 22 August 2010

Originally posted by: rocknroll

You cant just use it on its own, you have to use it in conjuction with data about power losses, harmonic currents and p.f.



Lets take some live data from a manufacturer;



400W lamp

20% control gear losses (in real terms this is more like 25% or 100W)

Harmonic current of 0.598A

Power factor of 0.9



If we do the calc using the recommended 1.8 factor all we need to do is,



400 x 1.8 / 230 = an Ib of 3A.



Now using the manufacturers data above,



400 + 100 (losses) / 230 x 0.9 (p.f.) = 2.4A



2.4A + 0.589A (harmonic current) = an Ib of 2.98A



How close is that then



Note that the 1.8 factor is only good for a power factor down to 0.65/0.7 after that then you need to use manufacturers data.



regards


Many thanks RnR for your time on this one.

Regards

Martin