Topic Title: Disconnection Times Topic Summary: Special Locations Created On: 06 October 2010 08:27 PM Status: Post and Reply |
Linear : Threading : Single : Branch |
Search Topic |
Topic Tools
|
|
|
|
|
Hi can anyone confirm if there is a reg that exists for the disconnection of a circuit fed by an MCB in a special location with a disconnection time of 0.2s looked in the regs book 17th 2008 & GN7 and cant find it anywhere if it exist please would give us the reg ref.
(the above query is for a MCB, fully aware of the use of RCD) Regards Martin |
|
|
|
|
|
|
|
|
There is no requirement for 0.2 sec disconnection; except table 41.1 for TT installations. Final circuits up to and including 32A. This is not specific to bathrooms though.
------------------------- http://www.niceic.biz |
|
|
|
|
|
|
|
|
Thats cleared that on up.
many thanks KJ regards martin |
|
|
|
|
|
|
|
|
There used to be 0.2s disconnection for some special locations in previous editions of the regs.
- Andy. |
|
|
|
|
|