 25 February 2010 10:59 AM
User is offline View Users Profile Print this message



micdem

Posts: 3
Joined: 25 July 2008

The 17th edition calls for 400/230V power and gives tables for maximum allowed EFLI values at ambient temperature.
We are testing 16th edition installations and the supply voltage is still 415/240V. In addition the testing is performed with live/loaded circuits.
Question: Which maximum EFLI values should we record on the test sheets?
 25 February 2010 12:09 PM
User is online View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17599
Joined: 23 March 2004

The 17th edition calls for 400/230V power and gives tables for maximum allowed EFLI values at ambient temperature.


It gives the values at thier permitted operating temperature.

We are testing 16th edition installations and the supply voltage is still 415/240V. In addition the testing is performed with live/loaded circuits.


The values are given for 230V and take into account the permitted opearting temperature as above. You don't need corrections for the maximum permitted value - only for your actual value for comparison purposes

Question: Which maximum EFLI values should we record on the test sheets?


The ones published in the edition of BS 7671 you are testing to. I presume this is an EIC for a legacy installation - if not you should be testing to the current edition anyway

OMS

-------------------------
Failure is always an option
 25 February 2010 02:33 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9806
Joined: 13 August 2003

supply voltage is still 415/240V

Is this outside of the UK/EU then?

- Andy.
 26 February 2010 08:09 AM
User is offline View Users Profile Print this message



micdem

Posts: 3
Joined: 25 July 2008

Originally posted by: AJJewsbury

supply voltage is still 415/240V


Is this outside of the UK/EU then?



- Andy.