Hi to every on the forum,
The company i workfor has invested in a Victron Pheonix inverter compact. The source is 12v dc-240VAC. The problem is that the manual states that the chassis has to be grounded. I have decided to do this by using earth spikes and an earth lead from the spike to a suitable ground. Because the inverter is to be a portable piece of kit, used for TV outside broadcasts, do i have to use special earth bond cable, as this will not be protected when in use. The distance of this lead will only be a few meters. I have looked in the 17th edition of the regs, and i couldn't see any thing about this in special installations. I welcome your input for any ideas on this topic or safety areas i need to look at. The AC output has an RCD fitted. Thanks. |
|
|
|
|
|
|
|
|
Have you looked at bs 7671 : 2008
reg 717.1 and/or 711.1 Not sure why you would need a special cable for the temp earth spike, other than it being flexible. |
|
|
|
|
|
|
|
|
See also BS7909.
I believe that there are cases stated in that standard, where vehicles are not anticipated to have a connection to earth ? ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
How would this product be used on the move
------------------------- James |
|
|
|
|
|
|
|
|
Well, now that's an interesting statement. What is actually meant by "grounding"?
In the EU (including UK), "earthing" means connection with the means of earthing, and/or with the general mass of the earth. The term "grounding" is not defined. But in the US, "grounding" is substantially what is meant by "earthing" in the EU. Conclusion: The "Chassis" of the vehicle is, strictly, neither "earth" nor "ground" unless you purposefully make that connection with the generall mass of the earth. Please be careful with answers at this point - my question has a purpose! ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
"Grounding " an American termology which defines a fixed voltage reference normally taken as 0V, not a direct connection to earth
Colin |
|
|
|
|
|
|
|
|
"Grounding " an American termology which defines a fixed voltage reference normally taken as 0V, not a direct connection to earth Colin Is that definition based on ANSI/IEEE standard reference, and/or National Electrical Code? Similarly in the EU I see instructions telling me to "earth" a suppressor to a motor casing - but the motor is part of a double-insulated machine . . . but we know that this is strictly an incorrect use of the term "Earth". I Quote from National Electrical Code Article 100 (Definitions): "Ground, the earth" "Gounded (Grounding). Connected (connecting) to ground or to a conductive body that extends the ground connection." etc. As far as I know, in the NEC, all references to "grounding" are connecting with the general mass of earth, as with "earthing" in the UK. ------------------------- Eur Ing Graham Kenyon CEng MIET Edited: 26 February 2010 at 09:15 AM by gkenyon |
|
|
|
|
|
|
|
|
I'm struggling to see why this piece of kit need referencing to earth.
We do that sort of thing with fixed mains installations becasue the remote source of energy is also referenced to earth. Shirly this just needs reference to the vehicle chassis? Paul ------------------------- "I learned very early the difference between knowing the name of something and knowing something". - Richard P. Feynman |
|
|
|
|
|
|
|
|
I'm struggling to see why this piece of kit need referencing to earth. We do that sort of thing with fixed mains installations becasue the remote source of energy is also referenced to earth. Shirly this just needs reference to the vehicle chassis? See Clause 7.4.2.3 of BS7909 "Where a generator supplies a temporary electrical system that is electrically separate from all other electrical systems, a connection from the generator to the general mass of earth is not essential. If this methos of supply is used, extreme care should be taken to ensure that there is no intended of casual interconnection with any other electrical systems, such as via earth referenced signal cables, CPCs, esposed or extraneous conductive parts." But caution is required with methods of protection and fault detection (i.e. failure of the separation) - normally it's more difficult to ensure electrical separation, than provide temporary earthing. There's a lot of information in BS7909: 2008, in particular Annex C has a lot of information on earthing arrangements and temporary systems, and does cover broadcast etc. vehicles. I don't think this is an easy topic. But the Original Post does contain a clue. If the manufacturer says it needs "grounding", than without other information, some kind of "earthing" is what's needed. See previous definition from National Electrical Code. ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
I'm struggling to see why this piece of kit need referencing to earth. We do that sort of thing with fixed mains installations becasue the remote source of energy is also referenced to earth. Shirly this just needs reference to the vehicle chassis? See Clause 7.4.2.3 of BS7909 "Where a generator supplies a temporary electrical system that is electrically separate from all other electrical systems, a connection from the generator to the general mass of earth is not essential. If this methos of supply is used, extreme care should be taken to ensure that there is no intended of casual interconnection with any other electrical systems, such as via earth referenced signal cables, CPCs, esposed or extraneous conductive parts." But caution is required with methods of protection and fault detection (i.e. failure of the separation) - normally it's more difficult to ensure electrical separation, than provide temporary earthing. There's a lot of information in BS7909: 2008, in particular Annex C has a lot of information on earthing arrangements and temporary systems, and does cover broadcast etc. vehicles. I don't think this is an easy topic. But the Original Post does contain a clue. If the manufacturer says it needs "grounding", than without other information, some kind of "earthing" is what's needed. See previous definition from National Electrical Code. ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
Hope you don't mind me giving you my take on this one. I can't help thinking some of you are reading far too much into it.
Grounding in the automotive industry means connection to the chassis ground. i.e vehicle chassis. Sounds to me like the metal body of the inverter (chassis), requires connection to the chassis of the vehicle (known as grounding) in order to prevent noise caused by what would be termed as Ground Loops! Which is basically electrical interference otherwise known as alternator whining. Hope this helps V Sorry, should have said such as alternator whining amongst others! Edited: 26 February 2010 at 11:03 AM by Veglen |
|
|
|
|
|
|
|
|
Hi Graham,
Thanks for your input on this subject. Ican see that this topic is causing quite a debate. I thought i would include the paragraph from the manual to clear any misunderstading with this grounding issue. "The neutral wire of the AC output of this inverter is connected to the chassis. This is to ensure proper functioning of the GFCI or RCCB to be installed in the AC output of the inverter. (i presume RCD is the same as a GFCI)? The chassis of the product must be connected to ground, to the frame of a vehicle or the ground plate or hull of a boat". These inverters are used a lot for marine use. I have e-mailed the company about this, but never recieved a reply, maybe they thought it was a stupid question! |
|
|
|
|
|
|
|
|
Hope you don't mind me giving you my take on this one. That point is: There are many uses of the term "earth", "ground" and "chassis", and combinations thereof, by manufacturers in their installation, operation and maintenance manuals, and sometimes by specifiers in designers in their documents. The problem is, these terms are meant in a variety of ways, often not really the way the terms "earthing" and "grounding" are defined in the relevant standards. And this mis-use causes the problem we've identified here. One answer "Just connect it to the Chassis Ground, it'll be OK" clearly contradicts the recommendations in BS7909 as I pointed out in an earlier post . . . is that OK? Would a court find it acceptable? The course of action for the Original Poster is: 1. Read and understand the relevant requirements in BS7909 and BS7671 2. Seek clarification from the Manufacturer. 3. Ensure that the appropriate requirements of the standards and manufacturer are incorporated in the design. Since this is Work Equipment in the UK, PUWER applies as well as the general obligations of Health & Safety at Work etc. Act. and the Electricity at Work Regulations. We need to be mindful, that in the UK, the duty to provide adequate earthing (where it is required for safety) in the Electricity at Work Regulations is an ABSOLUTE duty - you MUST do it, as opposed to "So far as reasonably practicable" that's a quailificaiton in some other parts of the Electricity at Work Regulations. See Regulation 8 of Electricity at Work Regulations. ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
Hi Graham, Thanks for your input on this subject. Ican see that this topic is causing quite a debate. I thought i would include the paragraph from the manual to clear any misunderstading with this grounding issue. Anyway, including this extract makes things a little clearer. The chassis of the product must be connected to ground, to the frame of a vehicle or the ground plate or hull of a boat". The problem is, this doesn't help you in the slightest, because the manufacturer is giving you the option, covering a very wide range of applications. The answer for you will, I suppose, depend on what the Outside Broadcast Vehicle is doing, and whether you feel you can ensure safety without providing an external "earth", if you connect to "chassis". This gets more complicated, if the vehicle has to provide power for equipment "off vehicle". I'd recommend you get hold of BS7909 "Code of practice for temporary electrical systems for entertainment and related purposes" which discusses these kinds of applications, as well as the relevant elements of Part 7 of the Wiring Regulations BS7671, dependent on the intended use of the vehicle (e.g. 711 and 717) Maybe also, need to put something in a "users' manual" for the vehicle - any labelling required etc.??? ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
Thanks gkenyon,
Are you talking about the requirements of section 717 in BS7671 or have I missed the point you are making all together? Sorry I don't have any info on BS7909. I have found some info that might be of interest and may be of some help to the OP. Installation manual for the Vectron Energy Phoenix Inverter Compact! Read section 4.3 Connection of AC cabling, Page 7 EN EN NL FR DE ES Appendi 4.3 Connection of the AC cabling This is a Safety Class I product (supplied with a protective grounding terminal). The neutral wire of the AC output of this inverter is connected to the chassis. This is to ensure proper functioning of a GFCI (or RCCB) to be installed in the AC output of the Inverter. The chassis of the product must be connected to ground, to the frame (of a vehicle) or the ground plate or hull (of a boat). Not for the reasons I suggested but, Ohwell! Hope this helps V Sorry gkeyon, You replied to nigel24 before I got my post in however, I'll let you carry on with your debate as it is getting a little too deep for me and follow with interest. Regards Edited: 26 February 2010 at 01:27 PM by Veglen |
|
|
|
|
|
|
|
|
Thanks gkenyon, Are you talking about the requirements of section 717 in BS7671 or have I missed the point you are making all together? My guess is, it's only 717 + BS7909: but without full details, can't make a decision. Installation manual for the Vectron Energy Phoenix Inverter Compact! Read section 4.3 Connection of AC cabling, Page 7 EN EN NL FR DE ES Appendi 4.3 Connection of the AC cabling This is a Safety Class I product (supplied with a protective grounding terminal). The neutral wire of the AC output of this inverter is connected to the chassis. This is to ensure proper functioning of a GFCI (or RCCB) to be installed in the AC output of the Inverter. The chassis of the product must be connected to ground, to the frame (of a vehicle) or the ground plate or hull (of a boat). ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
yes - Ground Fault Circuit Interrupter (much of the rest of the world have "interrupters" rather than "breakers") On the continent you tend to see various translations of "differential" instead of "residual", but the meaning's all the same. - Andy. |
|
|
|
|
|