rikhill
If subject to a small but permanent overload when (If at all) will an MCB trip?
From my reading of the time current curves in BS7671 they would seem to show a vertical line below approx 1.45ln so I would not expect them to ever trip.
On another thread rocknroll challenged this view and although I wasn't convinced by the physics presented I suspect he might be right and wondered whether anybody who enjoys playing with their test benches could settle it for me.
 23 February 2010 05:23 PM
AJJewsbury
Ah, but BS 7671 only shows the slowest allowable trip times (i.e. worst case for shock protection) - look at manufacturer's data (e.g. http://www.mkelectric.co.uk/Do...0Circuit%20Breaker.pdf ) and you'll see that there's an entire range of acceptable times for any given current.
 23 February 2010 05:37 PM
rikhill
Thanks Andy - Clearly a much easier to read graph than the BS ones, but that vertical line is still there (Just at 1.13 rather than my incorrectly assumed 1.45) - does that mean that a 6A type B running at 6.5A will hold for ever?
 23 February 2010 05:55 PM
perspicacious
"does that mean that a 6A type B running at 6.5A will hold for ever?"
Even 6.78 A
Hence 433.1
Regards
BOD