Hi folks
Just as the subject says really - does anyone know the max Zs for a BS1361 35A fuse? (It's in an old Wylex 1-way unit).
Unfortunately with fuses being non-linear I wouldn't have a clue how to start calculating it
Thanks in advance.
Stuart Reid
RED Electrical
http://www.redelectrical.co.uk
 26 January 2010 08:55 PM
rocknroll
1.92 @ 240V
1.84 @ 230V
Ref: Lawson Fuse Book!
"Take nothing but a picture,
"Oh! The drama of it all."
 26 January 2010 08:56 PM
stureid
Much obliged!
Stuart Reid
RED Electrical
 26 January 2010 09:20 PM
Inrush
The old Wylex data I have tends to disagree
I have a max current of 262 and 158 Amps for disconnection times of 0.4 and 5 seconds respectively, giving:
Zs (0.4S 230V): 0.87 Ohms
Zs (5.0S 230V): 1.45 Ohms
Interestingly there is a note which states:
'Protective device ratings 10A, 35A, and 40A are not in BS 1361. They are manufactured to the same requirements but then tested and certified to BS 88.'
 06 January 2013 09:00 PM
SherlockOhms
Was there ever a definitive answer to this one?
I have a similar 35A 88-1 in an old switch fuse unit feeding a shower.
I'd like to have some accurate date to use to convince the customer to upgrade.
Any more info on this would be appreciated.
S.
 06 January 2013 09:51 PM
Perhaps inrush's data is based on 80 percent value, that would ne in line with R&R's info. Shower will need to be at .4secs though.