Whats the armour size for a 16mm 4 core swa & where is it in the book? ,cheers
Jason
 09 December 2009 07:44 PM
OMS
What type of SWA - PVC is bigger than XLPE.
16mm2 4 core (XLPE) to BS 5467 or BS 6724 would be around 50mm CSA
Not in BS 7671 - you could try Appendix B of Guidance Note 8
Regards
OMS
Let the wind blow you, across a big floor.
 09 December 2009 07:47 PM
perspicacious
Is it being used for "bonding"?
Regards
BAD
 09 December 2009 07:50 PM
mitten
Regards
BAD
yes ,but could run a seperate 10mm
Jason
 09 December 2009 07:59 PM
OMS
Regards
BAD
Ouch -
OMS
 09 December 2009 08:03 PM
perspicacious
Well, I thought you were missing your SPARing partner since you mentioned GN8
Regards
BOD
 09 December 2009 08:06 PM
OMS
Nice one BOD