Topic Title: Cable reference method
Created On: 07 December 2009 11:49 AM
VIRCABLE
What if a cable has more than one relevant installation method?
E.g - First 10 mts of cable run in an insulated wall then clipped direct for remaining 10 mts.
I'm doing a periodic and it's a 40 amp MCB but 6mm2 cable. Some reference methods allow this, some don't.
Should you go by a 'worst case scenario' ?
 07 December 2009 01:25 PM
kermit1202
Yes
If more than one installation method, you should go by the worst case method.
you also put the worst case reference method in the box on the EIC or PIR on the schedule of thst results.
 07 December 2009 04:14 PM
GaryMo
I normally list both eg 102/C but obviously apply the worst case for cable selection.
 07 December 2009 06:56 PM
Avatar for Testit.
Testit
Yes I always go by the worst case too...
 08 December 2009 10:40 AM
VIRCABLE
Thanks lads