Topic Title: 4 pole rcds
Topic Summary: No Neutral
Created On: 15 October 2009 07:13 PM
bakey1959
Don't ask why, but we have ended up with 4 pole rcds supplying 3 phase + Earth sockets (no neutral).
Because of this, the test button on the RCD does not trip them and we have been told that it is possible and safe to connect a certain size resistor between the neutral and earth to facilitate this function. Does anyone know of such a practice?
 15 October 2009 08:39 PM
rocknroll
In the older RCD's the internal test resistor was connected between N and L2 or L3 so it was difficult to test a 3P + E supply.
Now the test resistor is placed in between the L2 and L3 pole so 2P + E, 3P + E and 3P + N + E supplies can be tested:
See;
http://i641.photobucket.com/al...cknroll/MWSnap186.jpg
(You will notice that the test resistor is connected between the L2 and L3).
If it is an older RCD (check manufacturers details first) then connect a resistor between the N and L1 terminal on the load side.
30mA RCD - 2200/2400 ohm 2 Watt resistor
100mA RCD - 1000/1200 ohm 2 watt resistor
Just a few more points:
I would remove the resistor after the test personally, the reason I said connect to L1 is because unless you have schematic of the RCD you dont know whether the manufacturer has connected the internal test resistor between N and L2 or L3 and this will cause an error, manufacturers dont connect the internal resistor to L1 so thats a clear pole for your test.
Remember this only a functional test to see if the mechanism works only.
"Take nothing but a picture,
"Oh! The drama of it all."
Edited: 16 October 2009 at 12:20 AM by rocknroll
 16 October 2009 05:00 AM
Go on then rock.
Someone had to ask.
Why the figures for the resistors?
 16 October 2009 10:38 AM
rocknroll
The resistors should give you a simulated fault current of around 1 - 5 Idn
30mA 30 - 150mA
230 / 2400 = 100mA (approx)
100mA 100 - 500mA
230 / 1200 = 200mA (approx)
George says: I = V / R
You could use a bit of wire and put the full system fault current across the RCD if you want but I suspect you could end up in casualty with a big-boned matron sitting on your chest trying to fish the test button out of your nose with a pair of long-nosed pliers.