I have a good knowledge of Ze calculations but when it comes to a typical use of a 240/110vac Transformer with 55-0-55 CTE Secondary, I come unstuck.

How do I calculate the impedence figures for the 110vac CTE secondary circuits.

I keep getting dragged into Transformer Regulation conversations.

Any help would be much appreciated.

Cheers,

Steve
 15 May 2009 07:22 PM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3490
Joined: 18 January 2003

Here is a starter.

Reflect the primary supply circuit impedance (Zp) into the secondary and then obtain the phasor sum of primary and secondary impedances .

Zsec = Zp *(Vs/Vp)² + Zpu (trans) * (Vs)²/VA + (R1 + R2) ohms

The first bit: Zp *(Vs/Vp)² reflects the primary impedance into the secondary

Next we take the Zpu (obtainable from the manufacturer) and convert the secondary impedance into a value:
Zpu (trans) * (Vs)²/VA

Finally R1 + R2 is the the resistance of phase and cpc for the secondary circuit (flex to appliance, etc).

I was on the BS 7375 (Distribution of electricity on building sites) committee and I did a lot of work on this - I don't have it to hand right now but if the above doesn't help post again.

EDIT: I have not checked my work on this yet, but I would expect that the above formula may need to be adjusted. As written it would appear to fail to take account of the fact that a fault creating an 'indirect contact' shock risk would only usually only involve half of the secondary winding, so a divisor of 2 may be required - I need to check.

The formula is taken from Paul Cook's Commentary but he gives a simplification that I do not agree with - this involves the earth fault loop path impedance for the primary circuit, rather than the line neutral impedance, which IMO is the correct method.

Regards

Geoff Blackwell

Edited: 15 May 2009 at 08:07 PM by GeoffBlackwell
 19 May 2009 10:27 AM
User is offline View Users Profile Print this message



bucephalus

Posts: 4
Joined: 15 May 2009

Geoff,

Many thanks,

For your information.

We use calculation software, either Amtech or CableCalc and neither deal with the 'Typical' scenarios we come across almost every day.

This being a 240vac single phase supply, with known Ze/PSCC figures, supplying typically a 2kVA 240/110vac (55-0-55)transformer, which goes on to supply a number of CTE sockets. (Portable equipment)

They tell us to treat the transformer as a 'load' say 12A primary current, and then calculate Zs (Ze+R1+R2).

This is where I am struggling.

I simplistically thought I could either get an impedence figure fromm the transformer vendor, and add it to the previously calculated Zs figure, which would form the Ze for the secondary calculations for the final circuits.

This may be '*****' and by the looks of it I would need to apply the formula you indicate.

Is Zp effectively my calculated Zs figure?
Is Zpu an Impedence Per Unit?

Clearly I am a bit of a 'dummy'!!!

Many thanks,

Steve
 19 May 2009 04:51 PM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3490
Joined: 18 January 2003

Zp is the impedance of the supply to the transformer primary. So it is the line - neutral impedance of the supply circuit rather than the line - earth impedance.

Zpu is the quoted per unit impedance (it might be given as a percentage). The figure I used in my research was 0.03 (or 3%) for a 10kVA transformer. This figure was given to me by a manufacturer.

Before you can apply all of this you need to determine the form of the output circuit.

The most likely fault would be one line to earth and this would involve just one half on the 110 volt transformer secondary (55 volts to earth). So IMO the Zpu should be divided by 2.

Note that a fault involving a short between both lines and earth would not produce any fault current in the cpc and, therefore, no touch voltage (I can prove this but that takes pages of calculations ).

That should get you started - I will post a sample calculation if I get time.

Regards

Geoff Blackwell
 19 May 2009 05:00 PM
User is offline View Users Profile Print this message



bucephalus

Posts: 4
Joined: 15 May 2009

Geoff,

Many thanks.
A sample calc would be greatly appreciated.

Steve
 22 May 2009 01:14 PM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3490
Joined: 18 January 2003

The first question I must ask is why do you want to know?

If it is because you think you must meet a 5 second disconnection time because the boys who wrote BS 7671 say so, I fear you have been misguided .

Those boys never did understand the principles of the shock protection provided by a Reduced Low Voltage System (RLVS). They also seem to ignore the work of Biegelmeier and Lee, and their own regulations . They continue to insist on a 5 second disconnection time for the RLVS. They even produce a nice table 41.6 backed by 411.8.3. They tell you that if you cannot engineer an impedance that is low enough to meet their nice table then you must use an RCD.

Think about it - that is use an RCD in a site transformer that gets dropped and kicked all over the place - yer that will work for a long time won't it. Still I expect the boys on site will test it often to make sure it works .

Now according to Biegelmeier and Lee (the touch voltage curve) if the touch voltage (indirect contact shock voltage) is less than 50 volts in dry conditions 95% of the population could tolerate the shock without injury (due to the shock). In wet conditions this would reduce to 25 volts.

According to BS 7671 - 411.3.2.5 - For a system with Uo > 50 volts - automatic disconnection is not required in the event of a fault to a protective or earth provide the output voltage of the source reduces to 50 volts or less within what would have been the required disconnection time.

Enter the RLVS - it can be shown (by some reasonably tough calculations involving such delights as superposition theorem) that under fault conditions the touch voltage on a RLVS instantly reduces to around 30 volts for some faults and zero for others. This even applies to the three phase version that has a Uo of 63.5 volts.

Given this you only need to disconnect to prevent fire and because it is good practice not leave a system in fault. Now the boys who wrote BS 7375 understood this and that standard does not specify any disconnection time.

The final joke is that BS 7671 Section 704 - 704.0 says that this section should be read in conjunction with BS 7375 - its a pity they didn't follow their own guidance .

Now why I am bringing all this up - well because it is at the heart of why you think you need to get a value for Zs. You will use this value to determine if a circuit meets table 41.6. This will impose restrictions on the maximum length of the circuit and in particular on the length of flex that can be used between .

If you fit RCDs to compensate how will you ensure that they remain operational?

If you do not impose such limits you will find that all but the most ridiculously long flexes will cause disconnection in a 'reasonable' time.

I will assume that you still feel the need to work out Zs so - to the calculations

I will divide the circuit into three sections. The calculations will be for a single phase system.

1) the supply circuit i.e the mains and the cable feeding the 110 volt transformer.
2) the 110 volt transformer.
3) the final circuit i.e the flex from the 110 volt transformer to the load (probably a power tool).

1) The supply circuit
This supplies the energy to the 110 volt transformer. It is this energy that would feed into a fault on the output side of the 110 volt transformer. We are not concerned with the supply circuit earth fault loop path as it is not involved in the system we are evaluating. We are concerned with the line to neutral impedance of the supply circuit as this will limit the flow of energy into the system.

We could determine this line to neutral impedance for the whole supply circuit if we measure it or calculate it, at the input terminals to the 110 volt transformer. This impedance consists of the line to neutral impedance of the DNO supply and the line and neutral resistance of the cable from the supply to the 110 volt transformer.

Lets call this Zp.

The value of Zp could be used directly in the complete calculation or, more commonly, it could be converted into an equivalent value that can be placed in the transformer secondary. This is a so called reflected value (reflected from primary to secondary) and we do this by multiply Zp by (Vs/Vp)².

Note that (Vs/Vp)² = (110/230)² = 0.23. So any primary circuit impedance only causes an effect equivalent to 23% of its value when reflected into the secondary. This tells us that the length of the supply circuit may not be all that significant in the overall results.

2) The 110 volt transformer
The windings of the transformer (primary and secondary) both have impedance and this will limit energy flow. Note that in calculations on transformers it is usually best to place all of the variables in either the primary winding or the secondary winding. The other winding then being assumed to be 'perfect' i.e to have zero impedance etc. I will place values in the secondary winding. This means that primary values must be reflected into the secondary.

A transformer manufacturer should be able to supply a value for the winding impedances and they will usually give this as a per unit quantity. This can be converted into a value for use in primary or the secondary - we will use it in the secondary.

The transformer impedance is given by Zpu * Vs²/VA ohms.

Zpu comes from the manufacturer and VA is the power rating of the transformer in volt-amperes.

3) The final circuit
This is the R1 + R2 of the flex from the transformer to the load. It should really be adjusted for the conductor temperature under fault conditions.

An example - we will use a 10kVA 230/110 transformer with a quoted Zpu of 0.03 and a CT secondary winding with a Uo of 55 volts.

The full load primary circuit current would be 10000/230 = 43.5 A. This gives us an idea of the size needed for the supply cable etc.

Lets assume that the line to neutral supply impedance is 0.2 ohms and that the cable from the mains to the transformer also has a line to neutral impedance of 0.2 ohms at full load temperature.

We could simply use the arithmetic sum of these impedances without too much error (the circuit will usually be mainly resistive) so we have:

Zp = 0.2 + 0.2 = 0.4 ohms

When we reflect this into the secondary circuit of the transformer we have:

Zp' = 0.4 *(Vs/Vp)² = 0.4 * 0.23 = 0.09 ohms

Next the transformer
Z(transformer) = Zpu * (Vs)²/VA = 0.03 * 110²/10000 = 0.03 * 1.21 = 0.04 ohms

Now this calculation includes the whole of the secondary winding but, in fact, if we consider a fault between a line conductor and earth on the secondary we would only be using half of the winding (55 volts to earth). So using a value for the whole winding will produce a higher impedance. The trouble is that the Zpu quantity also includes the whole primary impedance and this is required.

Now we could eliminate this error but it is probably not worth the effort. Leaving it will produce a higher figure and this error is on the right side for caution.

Bringing things together we have an impedance at the output terminals of the transformer of Zp + Z(transformer) and this is approximately:

Z (at output) = 0.09 + 0.04 (again just adding arithmetically) = 0.13 ohms.

Now bear in mind that this is for a 10kVA transformer - probably supplying a number of socket outlets. If we used a smaller transformer the impedance would be higher.

As I mentioned in the last post - Paul Cook simplifies the calculation a bit in his commentary - basically he ignores the transformer impedance. This is a valid approach and I used the same idea back in the mid nineties when I was on the BS 7375 committee. The error is not great as the transformer impedance will be mainly inductive and if we did the calculation correctly (i.e not taking simple arithmetic sums) it would not make much difference. The bit of his approach I disagree with is the use of R1 + R2 on the supply side of the transformer - IMO this should be R1 + Rn.

So now we get to the fun part - we are going to use our results to determine that maximum flex length between the transformer and the load (or you could say socket outlet close to the load).

Referring to BS 7671 table 41.6 - lets assume we have a 16A circuit protected by a 16A type C mcb. The table gives a maximum Zs of 0.34 ohms.

We have 0.13 ohms at the transformer so the flex can be R1 + R2 can be a maximum of:

(R1 + R2)flex = 0.34 - 0.13 = 0.21 ohms

Now using the data from GN3 for copper conductors

We have 12.10 milliohms per metre 20 degrees for 1.5mm² and 7.41 milliohms per metre for 2.5mm² now these would need to be multiplied by 1.2 to take account of conductor temperature and to match them to table 41.6. Note that these are just for one conductor so we need to multiply by 2 to get R1 + R2.

Maximum flex length will be:

Lmax = 0.21/((12.10/1000) * 1.2 * 2) = 0.21/0.029 = 7.24 metres

Oh dear, not very long is it

Well lets try a type B

(R1 + R2)flex = 0.69 - 0.13 = 0.56 ohms

Lmax = 0.56/((12.10/1000) * 1.2 * 2) = 0.56/0.029 = 19.3 metres

Better, but still not as long as some site flexes I have seen and we are using a type B - that could be a problem with motor loads

Remember we have used a fairly large transformer - it would be worse with a small one - still you could use RCDs but how long would they last

Better to bin your copy of BS 7671 and use the far superior BS 7375 .

Regards

Geoff Blackwell
 22 May 2009 01:27 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11270
Joined: 13 August 2003

The most likely fault would be one line to earth and this would involve just one half on the 110 volt transformer secondary (55 volts to earth). So IMO the Zpu should be divided by 2.

Doesn't it just come out in the wash if you divide Vs by 2? - i.e. use Vs = 55V (or 63.5V) rather than 110V.

- Andy.
 22 May 2009 01:34 PM
User is offline View Users Profile Print this message



bucephalus

Posts: 4
Joined: 15 May 2009

Geoff,

Excellent reply and I very much appreciate the time you have taken on my behalf.

We will be using BS88 fuses and the sockets will be hard wired for portable tools, but the method is clear now.

Regards,

Steve
 22 May 2009 01:44 PM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3490
Joined: 18 January 2003

Originally posted by: AJJewsbury

The most likely fault would be one line to earth and this would involve just one half on the 110 volt transformer secondary (55 volts to earth). So IMO the Zpu should be divided by 2.


Doesn't it just come out in the wash if you divide Vs by 2? - i.e. use Vs = 55V (or 63.5V) rather than 110V.

- Andy.


We are ultimately using the calculation against table 41.6 and this already uses the impedance divided into 55 volts. The value without a divisor contains an error because only half the secondary winding is actually in circuit.

That said, any error will be small as we would only have to adjust the secondary, and the winding is mainly reactive meaning that it has little effect on the overall result.

Regards

Geoff Blackwell
 22 May 2009 05:06 PM
User is offline View Users Profile Print this message



Erictrician

Posts: 155
Joined: 04 March 2007

This is a load of old tosh.

I do not know of anyone who has been electrocuted by a 55-0-55V system despite being used in some of the most appalling environmental conditions.

My advice is to go outside and enjoy the sun if you have nothing better to do.

Eric
 22 May 2009 05:55 PM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3490
Joined: 18 January 2003

Really - well its a good thing that some people spend some of their time making sure these systems are safe for you then isn't it.

Regards

Geoff Blackwell
 22 May 2009 06:11 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4437
Joined: 10 December 2004

Originally posted by: Erictrician
This is a load of old tosh.

I do not know of anyone who has been electrocuted by a 55-0-55V system despite being used in some of the most appalling environmental conditions.

My advice is to go outside and enjoy the sun if you have nothing better to do.

Eric


I am outside, enjoying the sun.
 22 May 2009 08:59 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 7374
Joined: 23 April 2005

Geoff

Thanks that was most informative. I takes me back to my college days talking about reflected impedances. What ashame most of that knowledge is locked away on inaccesible areas of my internal cranium hard drive.

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 23 May 2009 11:35 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3211
Joined: 13 July 2008

Geoff

What a contribution, Cheers.

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 25 May 2009 06:51 PM
User is offline View Users Profile Print this message


Avatar for rocknroll.
rocknroll

Posts: 8824
Joined: 03 October 2005

A couple of years ago after a request by a member who was taking an exam I posted a pdf on SH on how to calculate the loop impedance at the end of a circuit fed from the sec winding of a transformer, I included a step by step worked example, changing my computer to a Mac I downloaded all my files onto a load of DVD's but will look to see if I still have a copy over the next couple of days.

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------
 27 May 2009 08:13 AM
User is offline View Users Profile Print this message



kumaraguru

Posts: 3
Joined: 27 May 2009

Hi GeoffBlackwell,

Subject discussion : Building Design - Earth loop impedence
good day to you,

i have face problem with Earth loop impedence calculation.

Data input as

Trasformer 11000 /400 volts, Trasformer imp - 6.25 % (.0625 p.u.)

doing with amtech prodesign given as ZE of 0.0071 ohm. i have faced problem of Earth loop impedence error as



1.Cbl_FC-10 Zs=0.0706 Ohm

Max.Zs=0.0625 Ohm

Tef=28.68s Tefmax=5.00s The earth loop impedance Zs at the load end of the cable is 0.0706 Ohm > Max. Zs 0.0625 Ohm for the overcurrent protection. The Disconnection time Tef=28.68s exceeds the Max. time Tefmax=5.00s. Error



2. Cbl_SM-3 Zs=0.0396 Ohm

Max.Zs=0.0313 Ohm

Tef=36.21s Tefmax=5.00s The earth loop impedance Zs at the load end of the cable is 0.0396 Ohm > Max. Zs 0.0313 Ohm for the overcurrent protection. The Disconnection time Tef=36.21s exceeds the Max. time Tefmax=5.00s. Error

in the above Data 1 Error as (cb-fc-10) MCC panel located in Terrace . LV panel at basement Totally length shoul be 248 Mtr. Circuit protective device as 800 Amps ( 300 kw chiller .as per manufacture table starting current shall be 699 amps, reference : Trane chiller)

2.Data 2 Error as panel feeder supply from basement to 7th floor level . total length as 205 Mtr. Protective device as 1600 amps.


in manual calculation of Earth loop impedence

zs = ze+ ( r1+ r2)

ze - earth loop imp.
r1 - Phase Conductor Resistance
r2-Circuit Protective Conductor Resistance

in the above case i have connect from transformer to lv panel as bus duct of 2500 amps. length as 30 mtr.protective device as 2500 amps ACB.


kindly advice me how to claculate Earth loop impedence calculation.

await for your response .

thanks
kumaraguru

Edited: 27 May 2009 at 08:16 AM by kumaraguru
 27 May 2009 08:53 AM
User is offline View Users Profile Print this message


Avatar for GeoffBlackwell.
GeoffBlackwell

Posts: 3490
Joined: 18 January 2003

This is a detailed design and as such beyond what can be undertaken on a forum such as this. There are all sorts of issues such as PI insurance, etc, etc - not to mention that a designer would expect a considerable fee for all the work, and the risk .

You have not given sufficient data (transformer capacity (KVA) for a start.

I assume that you are not able to meet 5 second disconnection times as required by BS 7671. There are many solutions, but a good starting point would be to investigate what earth fault protection can be fitted as standard to your ACBs / MCCBs.

That is the best I can do I. BTW I don't use Amtech ProDesign.

Regards

Geoff Blackwell
 27 May 2009 12:10 PM
User is offline View Users Profile Print this message



kumaraguru

Posts: 3
Joined: 27 May 2009

Hi Geoff Blackwell ,

Thanks for your response,

i agree this is detailed design.

1. Transformer capacity shall be 1500 KVA. 11kv /400v, 50HZ, 6.25 % impedence. ( CPD rated as 2500 amps ACB ,50 ka icu, Electronic LSI)

From Transformer to LV panel utilised BUs duct 2500amps rated.

can you correct if i am wrong in earth loop impedence calc.

In earth loop impedence calc:

Zs= Ze +( R1 + R2)

Ze = 0.0071 ohms ( based on input from amtech result. R= .0014 ohm, X = 0.007ohm)

R1 =0.028 ohms
R2 = 0.126 ohms Here R1, R2 input values taken from Schneider catelogues, Canalis KTA.( because of Busduct used here)

Zs =0.1611 ohm

but my software calculation used in amtech prodesign as

LV panel at basement Circuit breaker rated as 1600amps.( connect to LV panel 7th floor . length as 205 Mtr)
LV panel at 7th floor circuit breaker 1600 Amps MCCB.

no earth fault protection can be fitted . just for amtech feed input as generic.


Even i have checked with BS 7671 Fixed equipment as 5 sec.
socket outlets etc., 0.4 sec.


here chiller as fixed equipment. ( cable 2Runs of 300 sq.mm CPD rated as 800 amps electronic LS)
but 7th floor LV panel incomer cable (4runs of 300 sq.mm ,CPD = 1600 amps MCCB electronic LS)

thanks & regards,
kumaraguru
 27 May 2009 12:38 PM
User is offline View Users Profile Print this message



Inrush

Posts: 694
Joined: 19 December 2007

Kumaraguru, what are you trying to ask?

As Geoff has already said what you are asking probably goes beyond the advice you are going to get on any forum, can you not consult another engineer at your workplace?

Also why can you not fit earth leakage protection to your MCCB?
 27 May 2009 01:00 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11270
Joined: 13 August 2003

Even i have checked with BS 7671 Fixed equipment as 5 sec.
socket outlets etc., 0.4 se

Sounds like you're looking at an out-of-date copy of BS 7671 too. The "fixed equipment" category disappeared with BS 7671:2008 (17th Ed).

- Andy.