Hi
I'am about to change a cosummers unit which is in a very tight space which can not be moved.
The problem is it is within the 150mm of the gas meter/pipework( the electricity service cut out is in the same cupboard (L 580mm X H 580mm X 580mm) and main earthing lead was recentley change by the network supplier with no comment.
My concerns are with (BS 6891:2005 installation of low pressure gas pipework in domestic premises, clause 8.16.2)
Because it is an exsisting old installation can the new consummers unit be fitted in place of the old and if so would I have to make a note on the Electrical Installation Certificate as the none compliance with BS6891:2005
 16 September 2008 04:57 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 7644
Joined: 04 July 2007

I wouldn't even condider it a problem, after all it's not a new installation is it, you're only replacing the existing d/b and if there's nowhere to move it to!
 19 October 2013 01:29 AM
User is offline View Users Profile Print this message



IHES

Posts: 1
Joined: 19 February 2013

Have been asked the same question by a plumber recently...
Consider also;

BS 6891:2005(2008)
"COMMENTARY AND RECOMMENDATIONS ON 8.16.1
The application of electrical insulating tapes should provide adequate protection where spacing is
impracticable."

I would consider
"Separation of at least 25mm to be provided for domestic pipework upto 35mm. For pipework over 35mm then 50mm separation is required"
To be Essential, and I would do everything reasonably practicable to ensure this is complied with.

If 150mm Separation between the gas meter and CCU is impossible to achieve i would note as a departure on the EIC


This is my first post on here....

Hope it helps


Paul Irelan-Hill
Irelan-Hill Electrical Services
 19 October 2013 01:17 PM
User is offline View Users Profile Print this message



BrucieBonus

Posts: 1018
Joined: 20 February 2007

I'd never do any domestic CU changes if I had to stick to that!
 19 October 2013 07:01 PM
User is offline View Users Profile Print this message



frspikeyhead

Posts: 830
Joined: 27 December 2004

If your finicky about these issues then stick a small piece of plasterboard between the two and separation is achieved. How you fix the plasterboard is entirely up to you.
 20 October 2013 02:49 PM
User is offline View Users Profile Print this message



24Hour

Posts: 262
Joined: 06 April 2006

Aggree with spikey,
Last time i found this, i could not find exact refrence in regs book, however in guidance notes, and if i recall building regs , it said to install barrier between the two, ie pink plasterboard.

-------------------------
Yes i do do 24/7 everyday of the FLAMIN year.
Statistics

New here?


See Also:



FuseTalk Standard Edition v3.2 - © 1999-2017 FuseTalk Inc. All rights reserved.

..