I am used to reducing the tabulated values max Zs in 7671 16th by 80% to alow for heat in the circuit. Now that the tables are calculated differently in the 17th, do i still need to reduce the new values by 80%?

NP
 02 August 2008 01:59 PM
User is offline View Users Profile Print this message


Avatar for Testit.
Testit

Posts: 2962
Joined: 06 August 2007

yep....

-------------------------
Online Services - http://propertydevelopment.org.uk

Experience can sometimes show that cost prevails over quality and safety, such little self-value that people hold.
 02 August 2008 02:35 PM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3538
Joined: 17 December 2004

By measurement
Zs(meas) <= 0.8 Zs(tab)

or by calculation
Ze + 1.2*(R1+R2)*L = Zs(Calc) <= Zs(tab)

(R1+R2 are taken from the tables in GN3 (and I assume, OSG 17th))
Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 02 August 2008 11:31 PM
User is offline View Users Profile Print this message



Pauldf1

Posts: 54
Joined: 09 May 2007

Just to confuse the matter, the figures in the back of guidance note 3 (2008 ed) appear to have been calculated by dividing the tabulated figure by 1.24.

(The 1.24(F) is given by the calculation F = 1 + (60 x 0.004) where 60 is the difference of conductor temperatures between max and measured and 0.004 is the simplified resistance coefficient of copper or alu.)
 02 August 2008 11:44 PM
User is offline View Users Profile Print this message



alancapon

Posts: 5842
Joined: 27 December 2005

Originally posted by: Pauldf1
Just to confuse the matter, the figures in the back of guidance note 3 (2008 ed) appear to have been calculated by dividing the tabulated figure by 1.24.


Yes, but dividing by 1.24 is the same as muliplying by 0.8065, which is almost 0.8. That is where we started.


Regards,

Alan.
 02 August 2008 11:50 PM
User is offline View Users Profile Print this message



Pauldf1

Posts: 54
Joined: 09 May 2007

Yep, x 0.8 is almost right. I just thought I'd add the / 1.24 as the figures don't match up with the ones in GN3 when you do the x 0.8 thing.
In the old GN3 they just used x 0.8.