Hello,
Our fixed installations are Earth bond tested when installed. I'm after guidance on Earth bonding existing applications on a regular basis. Is there a legal requirement for annual testing of equipment?
We contract work out on an annual basis for due diligence as panels could have been removed during maintenance ect...
I'm interested to know if there are legal requirements we need to adhere to.
Thanks.
 19 June 2017 05:09 PM
OMS
Legally speaking, it would be the Electricity at Work Regulations (if in the UK) - suitable and sufficient to prevent danger etc
Beyond that, I'm not sure what you are asking - is this testing of electrical equipment or the fixed installation ?
OMS
Let the wind blow you, across a big floor.
 20 June 2017 11:52 AM
broadgage
It is common practice to inspect and test the fixed installation every 5 years, and to test and inspect portable appliances every year.
Neither of these intervals are actually required by law, they are simply commonly regarded as good practice.
The law in the UK simply requires a safe system of work with risks eliminated or controlled so far as is reasonably practical.
In most cases it is up to the employer to decide what regime of testing and inspecting is required to comply with the law.
There are a few exceptions where test and inspection intervals are legally required, every 3 years in theatres I believe.
Also insurance companies, and in rented property the landlord or freeholder may specify test and inspection intervals.