Can a 10mm T+E take an induction hob of 6.4kw and a double oven 5.1kw?
 20 April 2017 08:57 PM
User is offline View Users Profile Print this message



weirdbeard

Posts: 3022
Joined: 26 September 2011

Appendix 4 BS7671 >

-------------------------
:beer)
 20 April 2017 08:57 PM
User is offline View Users Profile Print this message



geoffsd

Posts: 1523
Joined: 15 June 2010

Yes, so can 4 sq.mm. Method C with 32A MCB.

10 sq.mm is a sub-main for a flat.
 20 April 2017 09:19 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 7682
Joined: 04 July 2007

I would prefer 6.00 mm.
 20 April 2017 09:27 PM
User is offline View Users Profile Print this message



geoffsd

Posts: 1523
Joined: 15 June 2010

You old fashioned thing, you.

As above - Appendix 4.
 20 April 2017 10:00 PM
User is offline View Users Profile Print this message



mapj1

Posts: 8957
Joined: 22 July 2004

well, what size breaker is upstream of it, and what thermal insulation are you routing it through.
However unless it is extreme, almost certainly yes because Thermostatic controls conspire to keep turning ovens and cookers on and off after the first few minutes so the actual cable heating is much reduced over what you may imagine from the ratings. This is reflected in the advice alluded to above, which has many years pedigree..

-------------------------
regards Mike
 20 April 2017 10:34 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 15421
Joined: 13 August 2003

Can a 10mm T+E take an induction hob of 6.4kw and a double oven 5.1kw?

I work it out at 22A after diversity (presuming no socket outlet on the cooker control unit) - so at a push a 25A MCB and 2.5mm2 might suffice.
- Andy.
 20 April 2017 11:21 PM
User is offline View Users Profile Print this message



Alcomax

Posts: 110
Joined: 12 November 2009

For balance to the OP , cable routing must truly be method C to hedge your bets on <10mm. Insulation is everywhere is present build techniques. Downstairs kitchen, cable through joists and ceiling stuffed with insulation?