Topic Title: off topic. Trench Heating in offices
Topic Summary: water systems
Created On: 29 January 2013 07:39 PM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 29 January 2013 07:39 PM
User is offline View Users Profile Print this message



SKElectrical

Posts: 910
Joined: 01 February 2009

Are trench heating of water systems (not elec elements) piped as VT circuits or CT circuits. Thanks.
Can they be used as the sole source for a large open plan office?
Is there not a risk of high heels getting snagged?
 30 January 2013 08:54 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19763
Joined: 23 March 2004

Originally posted by: SKElectrical

Are trench heating of water systems (not elec elements) piped as VT circuits or CT circuits. Thanks.

Usually as CT circuits as they are designed for a particular function and are usually finned sections - so CT is optimum

Can they be used as the sole source for a large open plan office?

They could, but they wouldn't be too responsive as CT - usually they are used to deal with facade loss and offset to cold glazing radiation - the remaining space is then conditioned seperatly. In narrow plan well insulated structure they could be the sole source - but as they are limited in output (watts/m run) it's a bit unusual.


Is there not a risk of high heels getting snagged?

Depends on the grille section and if people need to actually walk on them - as true perimeter systems you wouldn't expect people to be walking that close to the facade.


OMS

-------------------------
Failure is always an option