Topic Title: voltage drop
Created On: 23 September 2011 08:57 PM
jonah71
A circuit is wired in 2.5mm pvc twin and earth cable and is 25 metres long, the current is 18 amps and the resistance is 0.37 ohms
Volt drop = I X R = V
18 x 0.37 = 6.66 volts
Where does the 0.37 come from ?
Volt drop for 2.5 is 18 mV/a/m
So i would work it out at 18 x 18 x 25 = 8.1
1000
Am I missing something ?
 24 September 2011 12:27 AM
eswnl
Can you repost to say:
What is the question, what variables are given and what is it you are asked to calculate?.
 24 September 2011 11:25 AM
Avatar for OMS.
The "volt drop" in mV/A/m is 18 at 70 C.
The cable has probably been measured at 20C - ie room temp
So:
Cable resistance at 70C = 18mV/A/m x 25m = 0.45 Ohm
Correction for the resistance measurement temperature from 70C to say 20C would be about 0.8
So - 0.45 x 0.8 = 0.36 Ohm (close enough to the stated 0.35 ohm)
Poor question really, because with 18A flowing through a 2.5mm2 cable it would be at approx 40C
Does that help at all
Failure is always an option